My electric furnace is in a small area enclosed by a louvered door. When the door is closed it blows warm air, when the door is open it blows hot air. This is a new problem, it used to work just fine whether the door was open or closed. Needless to say I cant check any voltages because the door is closed when it doesnt work right. Any suggestions on this problem would be greatly appreciated, thank you.
Have you checked your air filters for the furnace? When the door is open it is allowing more air to the unit. Is there something on the back of the door blocking air flow?
God, grant me the serenity
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
I do but it is not the problem, this unit worked fine until a couple weeks ago, it is a lack of air when the door is closed and something is not doing its thing then. I might add that I hear a clicking noise when the door is closed, whatever is doing that doesnt know which way to go.
If you have A/C, you also have an A-Coil that is in the airflow pathway.
Make sure it is clean and clear and allowing air through it completely.
The clicking is the Sequencer.
Take care and best wishes,
Robert
Make sure it is clean and clear and allowing air through it completely.
The clicking is the Sequencer.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I dont have any pictures to post, it is just a small area with a louvered door. I suspect a limit switch is getting too hot when the door is closed but dont know which one it might be. Short of replacing all three I dont know what else to do.
So your a/c is a self-contained unit with Evaporator Coil outside in Condenser Unit and not inside above your Furnace ?
If so, you could have a Limit that is weak and not holding.
IF you have no blockages through an a-coil or down in the duct and blower running full speed, then it is getting correct airflow.
If Limit is tripping, it is most likely weakened and just not holding.
When you suspect it is happening, you can turn power OFF, remove door and quickly test all Limits to see if any are open.
Remove wires and test for continuity.
Thanks,
Robert
If so, you could have a Limit that is weak and not holding.
IF you have no blockages through an a-coil or down in the duct and blower running full speed, then it is getting correct airflow.
If Limit is tripping, it is most likely weakened and just not holding.
When you suspect it is happening, you can turn power OFF, remove door and quickly test all Limits to see if any are open.
Remove wires and test for continuity.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 2 Replies
- 60298 Views
-
Last post by jazsimpson
Sat Jul 08, 2017 8:16 am
-
- 0 Replies
- 57573 Views
-
Last post by Montanan
Wed Jan 03, 2018 1:03 pm
-
- 0 Replies
- 50110 Views
-
Last post by Kourgath
Fri Mar 23, 2018 3:41 pm
-
-
LOUD Blower on Coleman Presidential 2 900759
by AuntKatie » Thu Apr 05, 2018 6:50 pm » in Coleman Service & Repair - 0 Replies
- 44830 Views
-
Last post by AuntKatie
Thu Apr 05, 2018 6:50 pm
-
-
-
Eb12eb Coleman furnace 4 speed help.
by Johnwayne892000 » Thu Aug 30, 2018 7:37 pm » in Coleman Service & Repair - 0 Replies
- 24988 Views
-
Last post by Johnwayne892000
Thu Aug 30, 2018 7:37 pm
-