We have a Nordyne Intertherm model E2EB-023HA Furnace/Blower inside and a Coleman BRCQ0361BD Condensor outside.
Blower works fine. The condensor hums then turns off but the fan will not turn on. The unit is hot to the touch. There is no freezing of the lines at either the a-coil inside or at the condensor outside.
Any suggestions?
Coleman Model BRCQ0361BD
Hi,
If contactor is pulling in and compressor is starting up and only problem is fan motor won't turn, try using a stick or ruler and shove fan blades.
If it starts up and turns then, probably a bad run cap.
If it still won't turn, need to see if it is getting full voltage to motor leads.
Can give parts /ordering info if the fault is found and it is needed.
Thanks,
Robert
If contactor is pulling in and compressor is starting up and only problem is fan motor won't turn, try using a stick or ruler and shove fan blades.
If it starts up and turns then, probably a bad run cap.
If it still won't turn, need to see if it is getting full voltage to motor leads.
Can give parts /ordering info if the fault is found and it is needed.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I turned the fans with a stick and the blades started back up but then after awhile they stopped. So it might be that run cap. What else would we need to order with that?
Hi,
If the motor stopped after a while, was the motor hot to touch ? It may be a bad motor also.
Need to know if motor leads were receiving full voltage when it quit again.
Having computer problems, sorry for delay in answering back.
Thanks,
Robert
If the motor stopped after a while, was the motor hot to touch ? It may be a bad motor also.
Need to know if motor leads were receiving full voltage when it quit again.
Having computer problems, sorry for delay in answering back.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Sorry, I didn't take off the top cover to notice if the motor was hot and i dont have a volt-meter so I am not sure if power was getting to the motor or not.
if the motor was hot would it be the motor being dead?
if the motor was hot would it be the motor being dead?
Hi,
If it is HOT, could be bad motor or insufficient airflow over motor such as a dirty condenser coil.
I can give ordering info for motor and run capacitor if you would like.
Just let me know.
Thanks,
Robert
If it is HOT, could be bad motor or insufficient airflow over motor such as a dirty condenser coil.
I can give ordering info for motor and run capacitor if you would like.
Just let me know.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 116536 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Nordyne model m1mb 070a bw power issue
by Combustibleink » Mon Nov 16, 2020 10:21 am » in Nordyne Service & Repair - 0 Replies
- 116192 Views
-
Last post by Combustibleink
Mon Nov 16, 2020 10:21 am
-
-
-
Evcon Heat Pump - Air Conditioner Model No. BRHS036B Making HUM Before Starting
by Dave_L » Tue Aug 29, 2023 1:26 am » in Coleman Service & Repair - 0 Replies
- 126602 Views
-
Last post by Dave_L
Tue Aug 29, 2023 1:26 am
-
-
-
Model DGAA070BDTA venting kit needed.
by spazatac » Fri May 24, 2024 11:21 am » in Coleman Service & Repair - 2 Replies
- 775 Views
-
Last post by spazatac
Mon Jun 10, 2024 3:11 pm
-
-
- 0 Replies
- 57616 Views
-
Last post by Montanan
Wed Jan 03, 2018 1:03 pm