This unit starts and runs just fine, But I do not think the flame is correct. There is blue right at the regulator outlet and lots of orange surrounding it. Seems to take a long time to heat the 1350 sq ft. home. Should there be any orange in the combustion area. There is no AC attached currently.
It is running on propane and propane configuration is in place
MIke
Model # M1MB-070A-BW
Hi,
Check your main burner orifice for blockage from spider/web . Should be blue with slight orange tip at most.
Thanks,
Robert
Check your main burner orifice for blockage from spider/web . Should be blue with slight orange tip at most.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Robert
we just got home, the burner was clean. I did spend more time looking at the flame. It is blue out of the burner, then when it strikes the plate it turns orange.
Also the temp coming out of the closest outlet was 101.
mike
we just got home, the burner was clean. I did spend more time looking at the flame. It is blue out of the burner, then when it strikes the plate it turns orange.
Also the temp coming out of the closest outlet was 101.
mike
Mike
Modular Unit in the Boonies
Modular Unit in the Boonies
Hi Mike,
Did you check the roof-jack and flue by any chance ?
What was the return air temp at furnace ?
Thanks,
Robert
Did you check the roof-jack and flue by any chance ?
What was the return air temp at furnace ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I think I might be wanting more from this unit than it is capable of. When we go up in the winter it is 40 inside the home and the air coming out the registers is basically warm. We also light the wood stove fire and withing two hours with both units going the temp it up to 73-75 in the living area.
square feet in 1350 with normal peaked ceilings. so have a lot of space to get warm.
square feet in 1350 with normal peaked ceilings. so have a lot of space to get warm.
Mike
Modular Unit in the Boonies
Modular Unit in the Boonies
Look on the data sticker or nameplate and see if it gives the designed temp. rise.
Usually, about 40* rise minimum, which would mean you should have another 10 to 12 degrees at least.
Thanks,
Robert
Usually, about 40* rise minimum, which would mean you should have another 10 to 12 degrees at least.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Then it is 15 to 17 degrees below normal supply minimum temp.
I would get a hvac tech out to look at it.
Thanks,
Robert
I would get a hvac tech out to look at it.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne model m1mb 070a bw power issue
by Combustibleink » Mon Nov 16, 2020 10:21 am » in Nordyne Service & Repair - 0 Replies
- 116168 Views
-
Last post by Combustibleink
Mon Nov 16, 2020 10:21 am
-
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 47679 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 116491 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Evcon Heat Pump - Air Conditioner Model No. BRHS036B Making HUM Before Starting
by Dave_L » Tue Aug 29, 2023 1:26 am » in Coleman Service & Repair - 0 Replies
- 126568 Views
-
Last post by Dave_L
Tue Aug 29, 2023 1:26 am
-
-
-
Model DGAA070BDTA venting kit needed.
by spazatac » Fri May 24, 2024 11:21 am » in Coleman Service & Repair - 2 Replies
- 741 Views
-
Last post by spazatac
Mon Jun 10, 2024 3:11 pm
-