have a Nordyne E1EB-015H furnace. I recently replaced all the parts in the furnace ( that I ordered from Mobilehomerepair.com of course) I wired everything per the wireing diagram but the problem is when I call for heat the blower comes on then the elements, and after shut down the blower shuts off before the elements, so I am assuming the the sequencers may have wires cross. where should I look first to fix this?
Thanks
Nordyne sequncing help needed
Hi,
Look at wiring diagram and be sure all is wired correctly. If wired correctly, blower should engage with first set of elements and disengage lastly.
Thanks,
Robert
Look at wiring diagram and be sure all is wired correctly. If wired correctly, blower should engage with first set of elements and disengage lastly.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I have double checked the wireing and it is wired per the diagram, but here is exactly what it does. When I call for heat the fan comes on right a way and I think the element comes on at same time but it may come on after the fan. but when the temp is reached the fan shuts off and I not quite sure if the elements shut off with the fan. but the element will come back on without the fan and after they trip the limit switch they shut off and stay off untill the furnace comes back on.. what can cuase this? Hope I explained it well enough
The two most common would be a bad sequencer or a wire or two crossed up. You said you have it wired right and parts are new though.
Would need to know which element comes back on, trace wire to sequencer and see if sequencer contacts are closed and if so, do you have 24vac at bottom coil terminals.
Thanks,
Robert
Would need to know which element comes back on, trace wire to sequencer and see if sequencer contacts are closed and if so, do you have 24vac at bottom coil terminals.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Model DGAA070BDTA venting kit needed.
by spazatac » Fri May 24, 2024 11:21 am » in Coleman Service & Repair - 2 Replies
- 782 Views
-
Last post by spazatac
Mon Jun 10, 2024 3:11 pm
-
-
-
Help with Nordyne electronic board
by swade1991 » Thu Aug 02, 2018 12:13 pm » in Nordyne Service & Repair - 0 Replies
- 33089 Views
-
Last post by swade1991
Thu Aug 02, 2018 12:13 pm
-
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 47704 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-
-
- 2 Replies
- 25849 Views
-
Last post by Maxwell.lipphardt
Mon Feb 04, 2019 6:35 am
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167503 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-