I have a Nordyne heater. Part of the time, the heater won't light apparently, because I notice it's not on and it has 4 blinnking red lights. Some of the time it lights and runs but the blower isn't working right. I"ve checked and the electronic ignition lights the pilot light. Then after a few seconds the fuel is pushed in and it lights. I will get a solid yellow light, and then after about 10 seconds the yellow light starts blinking. The flame keeps going until the blower starts. The instant the blower kicks on, the flame kicks off. After a few minutes it tries to kick on, but can't seem to stay on.
Nordyne heat constantly kicks off
Hi,
Check the main burner orifice to ensure there are no blockages such as a spider/web.
If ok and clear, then I would suspect the ignitor first and gas valve next.
The red blinking light is due to ignition failure and yellow blinking is due to weak flame.
You do not have a pilot light , the ignitor just ignites the gas as it comes through the burner.
Thanks,
Robert
Check the main burner orifice to ensure there are no blockages such as a spider/web.
If ok and clear, then I would suspect the ignitor first and gas valve next.
The red blinking light is due to ignition failure and yellow blinking is due to weak flame.
You do not have a pilot light , the ignitor just ignites the gas as it comes through the burner.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Posts: 16
- Joined: Mon Jan 05, 2009 9:26 am
- Location: Tennessee
I'll check that, but I've had nothing but problems with this unit since it was new 5 years ago.
One note about the pilot. I was watching this through the small flip cover at the front. I do have an electronic ignition that lights a pilot light. The pilot light stays lit for about 10 seconds before fuel is pushed through, which is then ingited by the flame. I don't know if it's not called a pilot light, but it's a small, eletconically lit flame that is about the same size as a cigarette lighter flame.
Anyway, I expect something els has gone bad. The first winter is the only winter I haven't had a problem with this unit.
One note about the pilot. I was watching this through the small flip cover at the front. I do have an electronic ignition that lights a pilot light. The pilot light stays lit for about 10 seconds before fuel is pushed through, which is then ingited by the flame. I don't know if it's not called a pilot light, but it's a small, eletconically lit flame that is about the same size as a cigarette lighter flame.
Anyway, I expect something els has gone bad. The first winter is the only winter I haven't had a problem with this unit.
Brandon
Hi Brandon,
Haven't checked, but you probably have a two step gas valve which opens at a low fire stage and then opens fully to full fire stage.
That would explain what you are seeing because there is no pilot or anything else for ignitor to light except the burner.
Take care and best wishes,
Robert
Haven't checked, but you probably have a two step gas valve which opens at a low fire stage and then opens fully to full fire stage.
That would explain what you are seeing because there is no pilot or anything else for ignitor to light except the burner.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Posts: 16
- Joined: Mon Jan 05, 2009 9:26 am
- Location: Tennessee
That sounds about right. Anyway, things have been hectic and I haven't had much chance to look at it, other than cleaning the filter. I'm suspecting the gas valve, since it burns until exactly when the blower kicks on. Of course there might be something wrong with the circuitry, but who knows. I'll be able to take a better look at it this weekend.
Brandon
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167390 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne M1B1 furnace issue - thermostat c wire not hooked up correctly. It's running off atteries instead
by Tallestt » Mon Apr 20, 2020 6:27 am » in Nordyne Service & Repair - 1 Replies
- 43347 Views
-
Last post by taurolyon
Tue Jun 23, 2020 4:02 pm
-
-
- 1 Replies
- 41999 Views
-
Last post by Greg
Sat Jan 06, 2018 9:11 am
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 116444 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Intertherm FEH-017HAC won't shut off
by Jetherid » Mon Dec 07, 2020 6:22 pm » in Nordyne Service & Repair - 0 Replies
- 175713 Views
-
Last post by Jetherid
Mon Dec 07, 2020 6:22 pm
-