Today my husband turned on the AC. He said that the house started to cool down. I arrived home at 7 pm and unit had been on since 4:30. Air was blowing through vents and outdoor fan was on but I could not hear compressor running. The refrigerant tubing inside was not cold. I am not sure how long unit was unning without the compressor or if it ever came on at all. Can you give me a check list to run down the cause of the compressor not running. (breakers, fuses, wires etc. and their locations relative to the indoor and out door units.) Also, how damaging was it to the unit for it to run that long with out the compressor? Thankfully there was no unhealthy sounding noises just felt and sounded like the fan was on.
You guys have been so helpful in the past. I don't know much about these kind of things but I have been able to make all repairs myself thanks to you guys.
Intertherm E2EB-017HA COMPRESSOR
Hi,
Contactor and compressor wires (outside condenser)
Run capacitorIndoor blower assembly
Compressor wires (outside at compressor)
High Pressure or Low Pressure switches if applicable. (outside condenser unit)
Compressor internal overload due to overheating. (internally inside the compressor.
Thanks,
Robert
Contactor and compressor wires (outside condenser)
Run capacitorIndoor blower assembly
Compressor wires (outside at compressor)
High Pressure or Low Pressure switches if applicable. (outside condenser unit)
Compressor internal overload due to overheating. (internally inside the compressor.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 65474 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-
-
-
Replace relay for Emergency. Heat in E2EB-15HB
by istvv4848 » Tue Oct 23, 2018 10:49 am » in Nordyne Service & Repair - 0 Replies
- 44294 Views
-
Last post by istvv4848
Tue Oct 23, 2018 10:49 am
-
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 55164 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 74933 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 116493 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-