I have a 1994 model furnace that when thermostat calls the furnace goes through pre-purge, the ignitor glows and the main burner lights. After a short period of time the gas valve starts clicking and does this for a random amount of time and will eventually go out. I have replaced the module, gas valve and cleaned the flame senser. When I trouble shoot the module, I have 94 volts present at the flame sense terminal and when the burner is lit when I go from this terminal to ground, the flame goes out everytime....where do I go next
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

Recheck the furnace model number last letter. There is only a BDC, BDD, BDE and BDF shown in our database.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
SteveH
Posts: 2
Joined: Thu Feb 04, 2010 9:40 pm

You are right the last letter is a C
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Did you clean the sensor with steel wool ? You test the flame sensor for micro amps, not volts.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?