Ok Guys,
This is what I got; Nordyne, Model number MGBA-056ABFC-01, Serial- MGB9405-00677. The Pilot will lite and stay lit while in the Pilot positon. However, Once I put it to the on position, the furnace will kick on, but the fan blows out the pilot. The Little woman is getting tired of it. HELP
Pilot Won't stay lit when in the run position
Hi,
Check pilot burner/orifice, pilot tubing for blockage. Make sure thermocouple is positioned correctly.
If all ok, replace thermocouple. If it does not resolve it, then need an hvac tech to test gas valve .
Thanks,
Robert
Check pilot burner/orifice, pilot tubing for blockage. Make sure thermocouple is positioned correctly.
If all ok, replace thermocouple. If it does not resolve it, then need an hvac tech to test gas valve .
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
ok, I had a Technician check out the unit and he said the gas valve was bad. $250.00 later, he said the Heat exchanger was cracked and I would need a new furnace. I pulled the entire unit out and disasembled it. There was no crack in the unit at all. There was, however, ALOT of soot in the bottom of the heat exchanger. any suggestions? Thanks
Hi,
Clean it thoroughly, inspect again and if no crack found, call hvac tech out to show it to you.
If in the end you're sure there is no crack, reinstall and see if unit works.
Thanks,
Robert
Clean it thoroughly, inspect again and if no crack found, call hvac tech out to show it to you.
If in the end you're sure there is no crack, reinstall and see if unit works.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Colman evcon presidental 7980B856 furnace will not stay on
by ezridersid » Sat Dec 21, 2019 8:52 pm » in Mobile Home Repair - 1 Replies
- 17318 Views
-
Last post by ezridersid
Sat Dec 21, 2019 9:04 pm
-
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 55210 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 74963 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
- 2 Replies
- 20960 Views
-
Last post by TorstenW
Tue Mar 06, 2018 1:04 am
-
-
Intertherm FEH-017HAC won't shut off
by Jetherid » Mon Dec 07, 2020 6:22 pm » in Nordyne Service & Repair - 0 Replies
- 175839 Views
-
Last post by Jetherid
Mon Dec 07, 2020 6:22 pm
-