Hi, when starting my ac for the first time this year i have been having some problems. Sometimes the ac just will not stop and i will find it down to 55 degrees before i can flip the breaker. I have tried changing the thermostat, it is a 2 wire so also tried directly connecting and disconnecting the 2 wires and it does nothing. The only way to shut off the inside blower and outside condenser/fan is to flip the breaker. It does this every other day, not all of the time.
I have no problems with the heat, it works just fine. Just the ac gives me problems. Last year it happened a few times and just ignored it, but this year its doing it more often.
The number on the ac blower is- 7900-6821
The number on the control box is- 7900-305
The number on the lower furnace is- 7966-856
The number on the outside condenser is- 7830-901
I can replace the parts myself, I just dont know what is broken.
Thanks for the help!!!!
AC will not shut off on colman presidential II
Hi,
At the t-stat, did you remove both wires and leave disconnected and it still did it and it wouldn't shut off with both wires disconnected ?
If so, that rules out the t-stat.
Next would be the t-stat reversing relay inside the a/c control box at furnace.
Thanks,
Robert
At the t-stat, did you remove both wires and leave disconnected and it still did it and it wouldn't shut off with both wires disconnected ?
If so, that rules out the t-stat.
Next would be the t-stat reversing relay inside the a/c control box at furnace.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Posts: 3
- Joined: Thu Apr 23, 2009 8:39 pm
That is correct, plus i have tried several different t-stats and like I said the weird part is the furnace has never given me any problems shutting off, its just the ac.
Hi,
You should have two control boxes, one down lowest for heating and one above or mounted to front of blower housing for cooling.
The model number you gave does not show as valid.
Can you be sure it is correct and also that it is the a/c control box model number.
Need to see which thermostat reversing relay you have , as that is most likely your problem.
Go here and look on right side for T-Stat Reversing Relay # 7670 - 3071 :
http://www.mobilehomerepair.com/ColemanAC.html
That is the reversing relay shown for the a/c control box listed for your furnace. However, there are other control boxes and reversing relays that would work, so need to know which yours has.
Thanks,
Robert
You should have two control boxes, one down lowest for heating and one above or mounted to front of blower housing for cooling.
The model number you gave does not show as valid.
Can you be sure it is correct and also that it is the a/c control box model number.
Need to see which thermostat reversing relay you have , as that is most likely your problem.
Go here and look on right side for T-Stat Reversing Relay # 7670 - 3071 :
http://www.mobilehomerepair.com/ColemanAC.html
That is the reversing relay shown for the a/c control box listed for your furnace. However, there are other control boxes and reversing relays that would work, so need to know which yours has.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Colman evcon presidental 7980B856 furnace will not stay on
by ezridersid » Sat Dec 21, 2019 8:52 pm » in Mobile Home Repair - 1 Replies
- 17314 Views
-
Last post by ezridersid
Sat Dec 21, 2019 9:04 pm
-
-
- 1 Replies
- 42054 Views
-
Last post by Greg
Sat Jan 06, 2018 9:11 am
-
-
Intertherm FEH-017HAC won't shut off
by Jetherid » Mon Dec 07, 2020 6:22 pm » in Nordyne Service & Repair - 0 Replies
- 175831 Views
-
Last post by Jetherid
Mon Dec 07, 2020 6:22 pm
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 116536 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167495 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-