Hey guys, great site. I have been working on my furnace for a day or two and need some help.
I have an Evcon DGAT075BDF that is in need of help. The AC worked fine but when I went to turn the heater on...no dice. I was getting 3 flashes (Combustion air switch failed to close). I replaced the combustion air switch with a toggle switch to override the switch to test it. I left the "bad" combustion air switch attached to the 2 hoses coming from the combustion blower motor and the other going to the furnace.
Now the furnace will attempt to ignite the 3 times but fails each time. So I started checking the switches and solenoids. I metered the brown wires at the gas valve to see if I was getting the 24v. The ignitor will glow then I get 26.x volts at the gas valve. The furnace actually attempts to light with ~1 sec of flame and then the voltage at the solenoids drops. It drops as if the control board told it to drop due to a bad switch.
I then ohm'd the upper limit switch and the lower limit switch. they are both closed when the furnace voltage is off.
Does anyone have suggestions? I have a new combustion air switch coming my way but that in itself will not fix the problem. Is the control board bad? Does it require a vacuum/pressure source from the hoses?
Any help would be greatly appreciated. I can meter anything y'all ask so that there are objective measurements.
Thanks
Evcon DGAT075BDF Furnace not working
Well my combustion pressure switch came in. I think they may have sent the wrong one.
I ordered: 1 Coleman Furnace Air Pressure Switch 024-27666-000 -0.15.
They sent: Honeywell pressure switch (S1-32435972000). For use with models: DGAA & DGAH.
I am about ready to just call someone to fix this. Any ideas?
I ordered: 1 Coleman Furnace Air Pressure Switch 024-27666-000 -0.15.
They sent: Honeywell pressure switch (S1-32435972000). For use with models: DGAA & DGAH.
I am about ready to just call someone to fix this. Any ideas?
Hi,
The gas valve should have 24vac and be open for about 6 seconds, before it shuts down IF flame not sensed at burner.
Check burner tube and burner orifice/spud behind gas valve for blockages (spider-web-bug).
IF you have a remote flame sensor, clean it carefully with steel wool.
The pressure switch closes once it reaches set water column pressure.
Be sure combustion air pipe is not clogged or separated/leaking, combustion motor and wheel are clean and running strong and tubes are not clogged, kinked or loose.
Be sure ignitor is getting full 120vac for ignition cycle.
You did receive the wrong switch, will need to return it.
Correct switch is 024-27666-001 (new p/n).
Thanks,
Robert
The gas valve should have 24vac and be open for about 6 seconds, before it shuts down IF flame not sensed at burner.
Check burner tube and burner orifice/spud behind gas valve for blockages (spider-web-bug).
IF you have a remote flame sensor, clean it carefully with steel wool.
The pressure switch closes once it reaches set water column pressure.
Be sure combustion air pipe is not clogged or separated/leaking, combustion motor and wheel are clean and running strong and tubes are not clogged, kinked or loose.
Be sure ignitor is getting full 120vac for ignition cycle.
You did receive the wrong switch, will need to return it.
Correct switch is 024-27666-001 (new p/n).
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I do have a "sensor rod" as the diagram calls it. So I will clean that if I can get it out. Where exactly is the combustion air pipe? Would you happen to know the best way to remove the gas valve so that I can reach all the "internal" things?
Thanks!
PS: I hope your health issues get resolved.
Thanks!
PS: I hope your health issues get resolved.
Ok. I cleaned the orifice and sensor rod. The furnace has a flame for ~2 seconds and then drops out. I do not know what the combustion air pipe is so that has not been checked. Also I have the air switch out completely since I am using a toggle switch to skip it right now, that means the 2 tubings are open to ambient air.
Any ideas what would make the burner fire for 2 seconds and then stop?
Thanks
Any ideas what would make the burner fire for 2 seconds and then stop?
Thanks
Bad sensor rod possibly. Sensor rod not positioned correctly.The combustion Air Pipe is pie connecting to top of booster motor assembly.
To bypass pressure switch for test run for a short while only, just jumper the switch terminals.
That is a safety switch however and should not be bypassed long or more than once.
Health issues will be here til the end, just have to live with them.
Thanks,
Robert
To bypass pressure switch for test run for a short while only, just jumper the switch terminals.
That is a safety switch however and should not be bypassed long or more than once.
Health issues will be here til the end, just have to live with them.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167397 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Colman evcon presidental 7980B856 furnace will not stay on
by ezridersid » Sat Dec 21, 2019 8:52 pm » in Mobile Home Repair - 1 Replies
- 17306 Views
-
Last post by ezridersid
Sat Dec 21, 2019 9:04 pm
-
-
- 1 Replies
- 39246 Views
-
Last post by Greg
Fri Apr 20, 2018 5:11 pm
-
- 2 Replies
- 27495 Views
-
Last post by plumducky
Tue Dec 10, 2019 3:59 pm
-
- 0 Replies
- 32628 Views
-
Last post by clsmatHH
Wed Oct 16, 2019 12:43 pm