I wrote last year regarding an intermittent blower issue with my Coleman 2865-666 furnace. After replacing the fan and limit switch, we had an HVAC company come out. They recommended that we replace the ICM. The unit originally had a Fenwal, but I was told that they did not have one in stock and that I could use a Honeywell S8610U which is a universal.
I installed the Honeywell which finally fixed my intermittent problem. However, a side effect is that now, occasionally, the ignition is extremely loud. I started reading through the manual for the Honeywell to make sure that I installed it correctly and came across a statement indicating that the unit should not be used for direct main burner ignition. My question is kind of two part:
1.) Is my Coleman a direct main burner ignition. I don't think that there is a pilot valve.
2.) How can I check if the Honeywell is operating properly? When I connected the wiring from my Fenwal, the Valve wire ended up only working on the PV terminal. However, I am getting 24 V AC when the valve is called to open.
Thanks for whatever help you can offer.
Brian
Coleman Model 2865-666 ICM replaced...loud ignition
Hi Brian,
You have an intermittent pilot system with an ignition module and an electrode.
Here is a tech sheet for the module:
http://customer.honeywell.com/techlit/p ... 8-0135.pdf
Thanks,
Robert
You have an intermittent pilot system with an ignition module and an electrode.
Here is a tech sheet for the module:
http://customer.honeywell.com/techlit/p ... 8-0135.pdf
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Thanks for the reply. The ignition is loud to the point of making me uncomfortable with the way the Honeywell is working with my system. I think I would like to order the Fenwal if at all possible. Is the one you sell (373-23884-001 Ignition Control ) the replacement part for my Coleman 2865-666 furnace?
Thanks,
Brian
Thanks,
Brian
Hi Brian,
Yes. Ignition Control # 373-23884-001 can be seen and ordered from here by paging down :
http://www.aberdeenhomerepair.com/store ... -2940-3251
Thanks,
Robert
Yes. Ignition Control # 373-23884-001 can be seen and ordered from here by paging down :
http://www.aberdeenhomerepair.com/store ... -2940-3251
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
LOUD Blower on Coleman Presidential 2 900759
by AuntKatie » Thu Apr 05, 2018 6:50 pm » in Coleman Service & Repair - 0 Replies
- 44830 Views
-
Last post by AuntKatie
Thu Apr 05, 2018 6:50 pm
-
-
- 2 Replies
- 25257 Views
-
Last post by Mark440
Sun Apr 28, 2019 12:48 pm
-
-
Unit Starts then Stops - Ignition Failure
by Arkady78 » Wed Dec 02, 2020 9:58 am » in Coleman Service & Repair - 0 Replies
- 104713 Views
-
Last post by Arkady78
Wed Dec 02, 2020 9:58 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 116444 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Nordyne model m1mb 070a bw power issue
by Combustibleink » Mon Nov 16, 2020 10:21 am » in Nordyne Service & Repair - 0 Replies
- 116112 Views
-
Last post by Combustibleink
Mon Nov 16, 2020 10:21 am
-