I have this unit installed in my garage. It has run great for a couple of years now. This winter though i am finding it pretty much comes on and shuts off when it wants to, usually running at night. I tried taking the t-stat off and just jumping the wires, but no go.After i turn the unit off and power it up, it goes thru the normal start up sounds but then wont fire up and i have 2 flashes on the indicator light. sounds like an igniter but am not sure. Can it be too dusty? The intermittent problem has got me on this forum....any help would be great!
Steve
Coleman DGAA07OBDTA
-
- Posts: 67
- Joined: Fri Nov 12, 2010 10:45 am
If you look on the control box cover behind the top panel, there should be a diagnostic code chart to tell you what the two flashes indicate. On my DGAT model furnace, two flashes indicate the centrifugal switch on the combustion air blower motor housing is stuck open.
"Man...that blowed up real good!"
Turn furnace off or set t-stat for a no-call for heat. Take a volt meter set for ohms/resistance testing. Remove one wire from pressure switch and test across for continuity.
Pressure switch is round disc shape with 2 wires and 2 tubes attached mid way of furnace.
2 flashes is pressure switch failed closed.
Thanks,
Robert
Pressure switch is round disc shape with 2 wires and 2 tubes attached mid way of furnace.
2 flashes is pressure switch failed closed.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Steve,
It is N.O. and should open at end of each cycle. Your diagnostic code is saying it is staying closed.
You should not have continuity once it is off. Testing will verify the flashing code. By the code, it should show continuity if it is indeed stuck closed.
Thanks,
Robert
It is N.O. and should open at end of each cycle. Your diagnostic code is saying it is staying closed.
You should not have continuity once it is off. Testing will verify the flashing code. By the code, it should show continuity if it is indeed stuck closed.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Robert,
Here is the latest i have found. Turned on furnace, blower motor goes on, some clicks from the control board. More clicks and the ignitor starts glowing. 5 seconds later ignitor stops glowing. It repeats this cycle a couple of times and then shuts down leaving the indicator light blinking twice.
Any thoughts?
Here is the latest i have found. Turned on furnace, blower motor goes on, some clicks from the control board. More clicks and the ignitor starts glowing. 5 seconds later ignitor stops glowing. It repeats this cycle a couple of times and then shuts down leaving the indicator light blinking twice.
Any thoughts?
Need to be checking at ignitor wires for 120vac from call for heat until ignitor goes out. See if it gets the 120vac within 30 to 45 secs. or so and then does it lose the 120vac when it goes out after just 5 secs. glowing ?
Thanks,
Robert
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Robert,
I just tried starting the furnace 10 times. 8 of the times the only thing that came on was the draft inducer motor, then 2 flashes on indicator. 2 times though after about 15 seconds of draft inducer running I heard a click and the ignitor started getting 120vac to the wires. after about 20 seconds it started glowing red then i heard another click like it was time for flames to start but nothing and after 2-3 seconds the ignitor stopped glowing and it stopped getting 120vac to it. then i am looking at 2 flashes again and back to square 1.
I just tried starting the furnace 10 times. 8 of the times the only thing that came on was the draft inducer motor, then 2 flashes on indicator. 2 times though after about 15 seconds of draft inducer running I heard a click and the ignitor started getting 120vac to the wires. after about 20 seconds it started glowing red then i heard another click like it was time for flames to start but nothing and after 2-3 seconds the ignitor stopped glowing and it stopped getting 120vac to it. then i am looking at 2 flashes again and back to square 1.
Make sure booster motor and wheel are clean and running good. Make sure air pipe to motor is not leaking and not loose , damaged or clogged.
Make sure the tubes from motor to switch are not clogged, loose or kinked.
Make sure there is always 24vac to one of the two pressure switch wires.
IF so and pressure switch never closes (should read 24vac across terminals and read 0vac when it closes).
IF it does not close, will need to call an hvac tech. Could be a few things wrong and will need testing to determine which one.
Thanks,
Robert
Make sure the tubes from motor to switch are not clogged, loose or kinked.
Make sure there is always 24vac to one of the two pressure switch wires.
IF so and pressure switch never closes (should read 24vac across terminals and read 0vac when it closes).
IF it does not close, will need to call an hvac tech. Could be a few things wrong and will need testing to determine which one.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 2 Replies
- 60295 Views
-
Last post by jazsimpson
Sat Jul 08, 2017 8:16 am
-
- 0 Replies
- 57572 Views
-
Last post by Montanan
Wed Jan 03, 2018 1:03 pm
-
- 0 Replies
- 50110 Views
-
Last post by Kourgath
Fri Mar 23, 2018 3:41 pm
-
-
LOUD Blower on Coleman Presidential 2 900759
by AuntKatie » Thu Apr 05, 2018 6:50 pm » in Coleman Service & Repair - 0 Replies
- 44829 Views
-
Last post by AuntKatie
Thu Apr 05, 2018 6:50 pm
-
-
-
Eb12eb Coleman furnace 4 speed help.
by Johnwayne892000 » Thu Aug 30, 2018 7:37 pm » in Coleman Service & Repair - 0 Replies
- 24987 Views
-
Last post by Johnwayne892000
Thu Aug 30, 2018 7:37 pm
-