RE: coleman presidential model #7966A856..........
Posted: Wed May 09, 2007 12:55 am
Turn ALL breakers to furnace OFF. Go to the Fan Switch and jumper across it. Turn breakers back on and set switches for Fan to run.
Did it run ?
Then, make sure all breakers are on and switches are on Heat and Auto.
Set t-stat to LOWEST temp setting, this should be enough to NOT get call for Heat.
Place meter leads across the 2 wire connections at t-stat, red lead on red and black lead on white. Your wire colors may vary.
Test for 24-28vac.
Let me know what you get.
There is another transformer in there somewhere, it should be in the upper box. What is that behind the bundle of wires to the left ?
It MAY be in outside Condenser Unit , but it is somewhere and will be 30 or 40VA.
This is sounding like a t-stat reversing relay or system switch failure.
Thanks,
Robert