Hi,
Not having 240vac could mean several things, but not a bad transformer.
Yellow and Orange wires.
Follow them to nearest connection point to see if there is 240vac there for them, 120vac to each one.
Thanks,
Robert
UPDATED**Nordyne/ No heat in auto-only in vent mode??
Was that while in the heat-auto mode ?
Are there any more connection points between the molex connector and the motor for those two wires ?
Does the motor leads end of the molex connector plug look ok inside ?
Thanks,
Robert
Are there any more connection points between the molex connector and the motor for those two wires ?
Does the motor leads end of the molex connector plug look ok inside ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi,
Look at the side of the motor and see if it shows the blower speeds with the wire colors.
IF the yellow is either low or medium low and orange is one of the line wires, then with 240vac at the plug, it should be getting to motor.
If so, then the motor would be bad.
Thanks,
Robert
Look at the side of the motor and see if it shows the blower speeds with the wire colors.
IF the yellow is either low or medium low and orange is one of the line wires, then with 240vac at the plug, it should be getting to motor.
If so, then the motor would be bad.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Robert, the wiring diagram shows the yellow wire to be motor low and the orange is going to the circuit breaker, so I have a bad motor?? If so it didn't last long, I just replaced this not 2 years ago, which one is it on the order page here, are there any cheaper alternatives? Thanks for all your help!
Set t-stat to call for heat and then with 240vac going to motor, reach in and spin blower wheel hard in correct rotational direction and see if motor starts running and runs complete cycle.
Thanks,
Robert
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hello Robert, did as you said, called for heat, had my meter leads in the yellow and orange wires going to the motor and gave the fan wheel a spin and got nothing.? If the motor is bad, is there just one speed in it( the one that I need fo heat) that is bad cause it works fine in "Cool" mode and "Vent", just not in heat? Thanks Robert, you've certainly been a huge help!
Hi,
Black = High = Cooling and Fan On Continuous
Blue = Med. High = nothing
Yellow = Med. Low = Heating
Red = Low = nothing
Orange = LINE = half of the 240vac (120vac/1 leg)
Try connecting the wire from board that is connected to yellow, try connecting it to the red wire.
THEN, if it works, take a reading at furnace return air grille and at nearest supply register to furnace for temps.
Low may be too slow, whereas Med. High would possibly be too fast.
Thanks,
Robert
Black = High = Cooling and Fan On Continuous
Blue = Med. High = nothing
Yellow = Med. Low = Heating
Red = Low = nothing
Orange = LINE = half of the 240vac (120vac/1 leg)
Try connecting the wire from board that is connected to yellow, try connecting it to the red wire.
THEN, if it works, take a reading at furnace return air grille and at nearest supply register to furnace for temps.
Low may be too slow, whereas Med. High would possibly be too fast.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi,
Yep, no board, was just one of those circuit board days. Remove yellow motor wire from molex plug and remove red wire also, then place red wire where yellow wire was.
Get a pocket thermometer and place it in furnace return air grille (louvered door) to get return air temp.
Then do same at the closest floor or ceiling register, whichever you have.
Thanks,
Robert
Yep, no board, was just one of those circuit board days. Remove yellow motor wire from molex plug and remove red wire also, then place red wire where yellow wire was.
Get a pocket thermometer and place it in furnace return air grille (louvered door) to get return air temp.
Then do same at the closest floor or ceiling register, whichever you have.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi,
Shouldn't hurt anything, you're just lowering heat speed from med. low to low. Most furnaces use the low speed for heating.
Check the return and supply temps to get temp rise and compare to data sticker or nameplate temp rise specs.
Thanks,
Robert
Shouldn't hurt anything, you're just lowering heat speed from med. low to low. Most furnaces use the low speed for heating.
Check the return and supply temps to get temp rise and compare to data sticker or nameplate temp rise specs.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167398 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Eb15a elec furnace will only come on if jumpered at themostat
by redcat31 » Wed Jan 31, 2018 6:18 pm » in Service & Repair of Other Brands - 0 Replies
- 23402 Views
-
Last post by redcat31
Sat Feb 03, 2018 1:20 am
-
-
- 1 Replies
- 3586 Views
-
Last post by Greg
Sun Oct 14, 2018 8:41 am
-
-
Doublewide - Vent or Leave roof Non-vented?
by 73Viking » Fri Jun 14, 2019 7:00 pm » in Mobile Home Repair - 2 Replies
- 11568 Views
-
Last post by 73Viking
Sat Jul 13, 2019 12:21 pm
-
-
- 3 Replies
- 3187 Views
-
Last post by Greg
Thu Aug 22, 2019 6:56 pm