coleman president no pilot
also have noticed the following : the 2 wires that come from the valve, one of these goes to a sensor, switch or something on the duct work up by the squirrl cage fan, this switch also has a small red button on it that seems to be sticking, i took it out and pused it up and down several times sometimes it works okay sometimes it sticks so you cant push it back up.cant find any numbers on it only thing i see is like T.P.O or something like that on the bottom where it goes into the duct work, the other side of this switch goes to another switch,(sensor) where this is a cluster of 2 of them on the lower side of the duct work.i am talikg about the exhaust duct work.
Hi,
Upper Limit Switch # 7624A3591 can be seen and ordered through PayPal from left side here :
http://www.mobilehomerepair.com/ColemanGas.html
The wire with the 13vac, where does it go to ?
As stated previously, I would replace the Hunter t-stat first thing.
Also, please stay with this until finished. I have received around 700 questions through the forums and private emails since you last responded.
I do not have enough time to be going back and reading everything again to refresh my memory, just too busy for that.
Thanks,
Robert
Upper Limit Switch # 7624A3591 can be seen and ordered through PayPal from left side here :
http://www.mobilehomerepair.com/ColemanGas.html
The wire with the 13vac, where does it go to ?
As stated previously, I would replace the Hunter t-stat first thing.
Also, please stay with this until finished. I have received around 700 questions through the forums and private emails since you last responded.
I do not have enough time to be going back and reading everything again to refresh my memory, just too busy for that.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
hey this gets better .i just looked to see if it was a 4 wire t stat to replace with your # 025-38747-000. and where the color code is this is how its wired . diagram say's green and yellow is attached,say's white and white is attached,say/s yellow and black is attached,say's r.h and red is attached,say's r/c and green is attached. what the h#* is this all about wired wrong ?? it worked fine last year, thanks again
How many wires are connected to it ?
Should have a red to RH, white to W, green to G and yellow to Y.
When the room temp is met and furnace keeps running, test t-stat W-White wire to ground for 24vac.
Thanks,
Robert
Should have a red to RH, white to W, green to G and yellow to Y.
When the room temp is met and furnace keeps running, test t-stat W-White wire to ground for 24vac.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
the wire that comes from the valve to the upper limit carries 13 vac room satified
room satisfied these are the readings on the t-stat:
thermostat says wire that is actually hitch volts
green yellow -0-
white white 2.7
yellow black -0-
r/h red 11.3
r/c green 28.0
room satisfied these are the readings on the t-stat:
thermostat says wire that is actually hitch volts
green yellow -0-
white white 2.7
yellow black -0-
r/h red 11.3
r/c green 28.0
-
- Posts: 31
- Joined: Wed Dec 24, 2008 11:42 am
- Location: Ohio
Title.
On a comical note: I thought the title of the thread meant; that the president of Coleman is a lousy pilot (as in boat or aircraft).bucklee wrote:coleman president no pilot
Hi,
Reading it now. Had a health hiccup, added onto by severe weather here and elsewhere and about 30+ emails/forum questions a day now.
With all that, haven't had time to pass gas, LOL and am a little backlogged.
Even had the heat quit at our other home we moved from and a gutter here broke and tore hole in overhang.
Who said you start slowing down at 50, LOL ?
Ok, let me see what you wrote.
Thanks,
Robert
Reading it now. Had a health hiccup, added onto by severe weather here and elsewhere and about 30+ emails/forum questions a day now.
With all that, haven't had time to pass gas, LOL and am a little backlogged.
Even had the heat quit at our other home we moved from and a gutter here broke and tore hole in overhang.
Who said you start slowing down at 50, LOL ?
Ok, let me see what you wrote.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi,
WITH room temp met and t-stat satisfied, at the W screw on t-stat, test that to ground for 24vac.
That is your heat power connection ad with t-stat satisfied, circuit should be open and you should have 0vac there.
Do you have a wiring diagram ?
Thanks,
Robert
WITH room temp met and t-stat satisfied, at the W screw on t-stat, test that to ground for 24vac.
That is your heat power connection ad with t-stat satisfied, circuit should be open and you should have 0vac there.
Do you have a wiring diagram ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 55202 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 74959 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
- 0 Replies
- 57616 Views
-
Last post by Montanan
Wed Jan 03, 2018 1:03 pm
-
- 0 Replies
- 50156 Views
-
Last post by Kourgath
Fri Mar 23, 2018 3:41 pm
-
-
LOUD Blower on Coleman Presidential 2 900759
by AuntKatie » Thu Apr 05, 2018 6:50 pm » in Coleman Service & Repair - 0 Replies
- 44876 Views
-
Last post by AuntKatie
Thu Apr 05, 2018 6:50 pm
-