I wanted to find out what SEER and exactly what ton rating my unit is.

I was told its a 4 ton unit, but just thought i would post this up to find out for sure.

My outside condensor unit us a Carrier. not sure what model thought, ill have to go take a look.


Thanks

RE: Coleman #3500A916

Posted: Tue Jul 24, 2007 12:42 am
by Robert
Hi,

The outside Condenser model number is needed for that. Can give tonnage then, but may not can get seer rating as it is not a normal MH unit.


Our database won't show Carrier info.


Thanks,
Robert

RE: Coleman #3500A916

Posted: Wed Jul 25, 2007 11:18 pm
by Guest
can you tell me the SEER rating on the coleman unit?

RE: Coleman #3500A916

Posted: Thu Jul 26, 2007 10:53 pm
by Robert
Hi,

The SEER rating is on the outside Condenser Unit. That being a Carrier, will need model number to try and get that.

The Coleman part is the furnace and has no seer rating.


Take care and best wishes,
Robert

RE: Coleman #3500A916

Posted: Sun Aug 05, 2007 11:51 pm
by Guest
OK, a new problem has developed and i figured id just post in this thread because it had my model number already posted.

I have a wood floor in my laundry room and you can tell where its been getting wet and we figured it was from the doggy door. Well tonite while my wife was doing laundry you can step on the floor and water comes up from the seems, so somethings up and it my a/c not draining.

i guess its running under the wall and under the floor, so i am going to have to pull up the floor and move out the washer and dryer and take a look, i already know we have some serious rot under the back door in the siding, im thinking its from the a/c.

Anyways i figure the drain pan under the a-coil is rusted out, but mine is plastic, the drain tube isnt clogged its just overflowing the drain pan.

Heres a couple pics i took, maybe you can give some advice based on them.

Image

see it seems to be seeping out from under the black plastic drain pan, and down a little channel behind the big black grommet and down next to the drain line and on the floor.

I took a video tape and put in under the plastic tray to angle the end opposite the drain up so it would force the water tawards the drain line, but this is a temp solution at best, and i need to know the best way to fix this perm.

Heres another pic i took a few minutes after it was running, after being shut down for about 20 min to clean up the mess on the floor.

Image

Im guessing the main problem is the pan being rusted out.

RE: Coleman #3500A916

Posted: Sun Aug 05, 2007 11:58 pm
by Guest
i just went and checked it out again, and im thinking my problem is the a-coil is freezing up, it starting to get a vertical strip of frost on both sides of the coil on the outside.

We had this problem whe we first moved in back in 03, and it was 4 pounds low on freon, guess its time to have the a/c man back to check it again.

RE: Coleman #3500A916

Posted: Mon Aug 06, 2007 12:12 am
by Robert
Be back in about 30 minutes to read and look over pics.


Take care and best wishes,
Robert

RE: Coleman #3500A916

Posted: Mon Aug 06, 2007 12:25 am
by hvac1000
A unit low on refrigerant and freezing up can cause a water problem. The coil when it defrosts will leak down the center and edges and miss the pan completely sometimes. This is because a proper operating coil will have water running down the coil strait to the pan. The ice on the coil causes the water to be diverted to other areas besides the plastic pan. I would also check to make sure the coil is clean of all dirt and foreign matter. There are instructions for doing this under the help tips posted on this board.

Robert also might have additional information on this subject since he works on mobile home equiptment all the time.

RE: Coleman #3500A916

Posted: Mon Aug 06, 2007 2:49 am
by Robert
Hi,

Sorry, I got sidetracked . Anyway, I'd say HVAC1000 is right on target.

Here are some articles to help get units clean:

http://www.mobilehomerepair.com/article ... ioner.html


http://www.mobilehomerepair.com/article ... lower.html



Four pounds is a fairly big amount and the leak should be located.


Then it can be repaired and a vacuum pulled before recharging.


Also be sure to change/clean filter every 30 days.


Remove the tape, that's to big of a slant.


You can tape a wet/dry vac hose to the end of drainline and pull out any blockages usually.


Make sure you have a trap in the drainline, preferrably as close to A-Coil as possible.



Drainline should be 3/4" CPVC or equivelant .



You can DIY all of above except finding leaks and repairing, pulling vacuum and recharging.


Take care and best wishes,
Robert

RE: Coleman #3500A916

Posted: Mon Aug 06, 2007 8:59 am
by Guest
thanks for the help, we had it cleaned real good by a pro last year, but the problem is its freezing up, after about an hour of running constanly we took the cover off and it looked like it had snowed in there.

Im guessing its low on freon again, i am going to call out a pro this afternoon, i can do auto a/c work all day long and have all the tools to pull vac and recharge, but never really messed with house a/c.