skirting

Posted: Thu Oct 17, 2013 10:24 am
by terrifromohio
I had skirting installed in August, they put a couple of vented panels at the end of the trailer but they look like they are blocked by another piece of skirting behind it, they did not put any other vented panels around the trailer or any other vents.
I am now having a huge moisture problem in the trailer, 75% moisture. Could this be causing all this moisture? They also did not vent the air conditioning line outside the trailer as it was before, it is laying under the trailer.
How many of these vented skirting panels should be around the a 14 by 70 mobile home to properly vent it?

Re: skirting

Posted: Thu Oct 17, 2013 6:02 pm
by Greg
You should have 1sq/ft of ventilation per 150sq/ft of floor space. That translates to a minimum of 6.5 sq ft. of ventilation for your home.

Greg

Re: skirting

Posted: Thu Oct 17, 2013 10:12 pm
by 1987Commodore
You mention an a/c vent; do you mean the condensation drip line? That should go outside. Make sure the dryer vent is outside the skirting also.

Re: skirting

Posted: Fri Oct 18, 2013 8:44 pm
by Greg
Good catch, I forgot that part.

Greg

Re: skirting

Posted: Sun Oct 20, 2013 9:01 am
by terrifromohio
yes that is one problem, the condensation drip line is underneath the trailer, when they put the skirting on they did not vent it outside. I was not here as I has a family member in the hospital at the time. They also did not put any vents in the skirting whatsoever.
In my mind if they ever installed skirting before they should have known better. Now I am having a hard time trying to get them to come back and fix it and it is starting to get cold. They charged me 1500.00 to do 14 by 70 in vinyl which I thought was a little high.