Evcon Natural Gas to Propane Switch Question

Posted: Sat Sep 15, 2007 8:36 am
by skyline1998
I have an Evcon, DGAT056 BDE w/air conditioner. I will be switching to propane from natural gas in a few weeks. The information on the inside of the furnace tells me: "For natural gas use orifice 29. For propane, use orafice 45". The little cloth bag attached to the valve contains a tag that says "Propane" and an orifice with .82 stamped on it. Is this the correct orifice?

Thanks,

Greg

RE: Evcon Natural Gas to Propane Switch Question

Posted: Wed Sep 19, 2007 1:27 am
by Robert
Hi,

Yes, for LP you use the #45 / 0.082 . It is correct one.

Remember, you also have to convert the gas valve or replace if non-convertible.

You also have to change the gas pressure and have burner flame

inspected and adjusted if needed.



Thanks,
Robert