Posted: Sat Sep 29, 2007 11:25 am
by elkman
I have a coleman evcon(can't find a model # ,the tag has faded)that the a/c fan has quit running on.I came home yesterday and the blower on the inside of the house was running and putting out warm air. I checked the outside unit and the fan is not running,although I can hear a humming sound inside the outside unit.The blades will spin freely on the motor ,just not running The part number on the fan is cpn-1468-412. and the unit is 12 years old.Is it just the fan or could there be other problems causing the fan not to run?

RE: evcon outside fan motor

Posted: Sat Sep 29, 2007 6:40 pm
by hvac1000
I would check your fuses/breaker outside in the disconnect. Then I would check the breaker in your electric panel on the inside of your home. Report back with your findings.

RE: evcon outside fan motor

Posted: Sun Sep 30, 2007 11:25 am
by elkman
Thanks for the advice.I checked the inside box and none of the breakers were kicked out. The outside disconnect box has a t pull switch with out any breaker.I pulled it out and examined it and put it back in and turned the unit on and the fan started running and I have A/C again!! I guess it must have gotten loose over time and was not making a good connection.

Posted: Sun Sep 30, 2007 11:42 am
by hvac1000
Glad you got it going. If it happens again you may check the wiring in the outside disconnect for tightness after you turn the breaker off in the home. This way there will be no electric going to the outside A/C disconnect when you are checking the wires.