Leaking water

Posted: Mon Oct 08, 2007 9:37 am
by jess214
I have a Intertherm model E2EB-012HA. Whenever the a/c is turned on water is leaking out from the right control panel cover. Does anybody know what could cause this?

RE: Leaking water

Posted: Mon Oct 08, 2007 8:21 pm
by Robert
Drip pan under a-coil overflowing, water being drawn out of drip pan, water being pulled off the a-coil surface, drain line being clogged up, drip pan leaking.


Make sure a-coil is clean and fins not damaged and make sure air is being pulled through the coil and not over and around it.


Leave unit off and fill drip pan to check for leaks. Also check for full drainage from drainline.



Take care and best wishes,
Robert