Page 1 of 1
Furnace won't ignite
Posted: Sun Oct 28, 2007 7:56 pm
by mallmon
Hello, I am new here, and I have looked around the site and found it to be fantastic. Lots of friendly advise and help. So this is my issue. Coleman Evcon gas furnace Mod- DGATO7OBDC is not igniting, I can see the glowing ignitor, but no burner. It cycles 3 times and gives up. Now I just bought this place and it has had plumbing and electrical issues, but I am going to be needing heat real soon. Any help is greatly needed, thanks.
Mike A.
RE: Furnace won't ignite
Posted: Sun Oct 28, 2007 9:08 pm
by Robert
Hi Mike,
It could be ignitor not energized completely, ignitor mounted away from burner, gas valve faulty, gas pressure problem, spider/web in gas valve to burner orifice.
On a call for heat, if the small booster motor starts within 2-3 seconds, then after a while the ignitor starts glowing, then one of the above is most likely the problem.
If you have a meter, test across the wires connected to gas valve and see if it is getting 24-28vac.
Thanks,
Robert
RE: Furnace won't ignite
Posted: Mon Oct 29, 2007 6:20 pm
by mallmon
Thanks Robert, I cleaned and checked the furnace, it is not getting the 24v to the gas valve. The booster motor starts but no volts to turn gas on. Is there something that I may have missed or do I need a Ignition Controler. Thanks.
Mike
RE: Furnace won't ignite
Posted: Mon Oct 29, 2007 9:53 pm
by Robert
Hi Mike,
Ignition Module : TH-------------GND = 24 VAC
VALVE---------GND = 24 VAC
Test across those, one lead on each and see if you get those readings WITH a call for heat.
Set t-stat to HEAT/COOL/85* for testing, this should give call for heat.
Thanks,
Robert
RE: Furnace won't ignite
Posted: Thu Nov 01, 2007 8:30 am
by mallmon
Hi Robert, Just got a chance to check these voltages, I had 26v at TH- ground and only .5v at valve- ground. Is there anything else that I should be looking for??
Thanks for the help.
Mike
RE: Furnace won't ignite
Posted: Thu Nov 01, 2007 3:03 pm
by Robert
Hi Mike,
Send me an email at
robert@mobilehomerepair.com .
Thanks,
Robert