Presidential II 7655-856 Burner Will Not Ignite
Posted: Mon Oct 29, 2007 11:52 am
by sherrien59
My Presidential II 7655-856 worked fine this past Spring. Since it is starting to get cool at night, I decided to fire the heater up. I lit the pilot light and it stays lit. However, the burner will not ignite. From the postings on this site, I figured out that I should start my troubleshooting with the transformer. I have ordered the part from you guys. Is there anything else I should be checking?
RE: Presidential II 7655-856 Burner Will Not Ignite
Posted: Mon Oct 29, 2007 3:04 pm
by Robert
Hi,
Did you test the transformer to see if it was bad before ordering ?
Did you test to see if you were getting 24 VAC to the gas valve wire connections ?
Have you checked the gas valve to burner orifice, small brass fitting at back of gas valve with small hole in center) ?
Turn the gas valve and gas pressure OFF to check it, it may be clogged with spider/web.
If unsure about any of this or uncomfortable, please call a Tech to look at it. Gas is not very forgiving.
Take care and best wishes,
Robert
RE: Presidential II 7655-856 Burner Will Not Ignite
Posted: Mon Nov 05, 2007 11:27 am
by sherrien59
I hooked up the new transformer that I ordered from you guys. The burner ignited and the fan kicked on and now I have a toasty-warm mobile home again.
Just wanted to let you know how much I appreciate your website, Forum, Store and your assistance. I would much rather troubleshoot something myself and do what I can before having to pay someone to do something I'm not able or qualified to. Thanks.
RE: Presidential II 7655-856 Burner Will Not Ignite
Posted: Mon Nov 05, 2007 11:49 am
by Robert
Hi,
You're very welcome, glad it is warm again in your home.
Thanks for ordering and the kind words.
Take care and best wishes,