nordyne E2EB-012HA

Posted: Wed Oct 31, 2007 10:33 pm
by bypass10
had smoke coming out of the left side bottom of unit,
opened it up to the left of the heating coils their appears to
have been a thermostat of some type i think 4 wires attached
the part was burned into nothing that i could really identify
any help like part type and nbr would be appreciated.

RE: nordyne E2EB-012HA

Posted: Wed Oct 31, 2007 10:39 pm
by Robert
Hi,


Most likely a limit switch, so with it burnt, need to have the amperages tested to find reason for burn.


You also have a sequencer in there, but more than 4 wires attached.


With burnt parts, it can be deceiving.


How many terminals does it have, can you tell ?



Take care and best wishes,
Robert