DGAA090BDTA coleman

Posted: Fri Nov 02, 2007 11:23 pm
by monotonetruth
hey I'm working on a furnace Coleman DGAA090BDTA and its telling me that the pressure switch is bad. with a little suction i can hear the switch work so i am wondering if it could be something else or if the switch is bad, or how i can tell what it is exactly????

RE: DGAA090BDTA coleman

Posted: Sat Nov 03, 2007 3:18 am
by Robert
If it says the pressure switch, it could be the switch itself, the booster motor, the tubes, the air pipe causing switch to not close.


You would have to test the water column pressure to see if it is switch or motor.


Thanks,
Robert

Posted: Sat Nov 03, 2007 9:37 am
by monotonetruth
how do i test the water column pressure? ...... i have checked the tubes, and they are like new. and it sounds to me like the booster motor is running just fine.

RE: DGAA090BDTA coleman

Posted: Mon Nov 05, 2007 7:59 am
by Robert
You would need special tools and equipment plus experience to test for that.

Test the pressure switch and see what voltage it reads across the two connections.

Does it read 24VAC and then drop to 0VAC or does it read 24VAC always ?


If it reads 24VAC at all times and booster motor sounds to be running full speed, most likely the switch.


Without a Tech to test it, you would have to decide whether to replace switch or not.


Thanks,
Robert

RE: DGAA090BDTA coleman

Posted: Sat Nov 10, 2007 7:24 pm
by monotonetruth
Thank you very much for all the help, we ordered the pressure switch (from your site) and installed it. bingo .....the furnace worked. so thanks again for the help.

RE: DGAA090BDTA coleman

Posted: Tue Nov 13, 2007 7:11 am
by Robert
Hi,

You're very welcome and thank you for the kind words and for ordering with us.

Glad it is working again.


Take care and best wishes,
Robert