InterTherm E2EB-012HA problems

Posted: Wed Nov 07, 2007 9:29 pm
by sephiek
the problem with my intertherm unit is that. with the thermostat
controls set to auto and the cool or heat selector switch set to the off position, the heating elements are still active and heating, the
elements will turn off when i shut down the breakers inside the unit, but when i turn the breakers on the heating elements turn on to... if i set the controles to heat and to the auto possion, i can run the temp setting up above room temp and the fan and heat will work ok. but as soon as the room temp gets to the set possion, the fan will turn off but the heating elements will not.

RE: InterTherm E2EB-012HA problems

Posted: Thu Nov 08, 2007 10:31 pm
by hvac1000
Sounds like a defective heat sequencer.

RE: InterTherm E2EB-012HA problems

Posted: Sat Nov 10, 2007 8:43 am
by Robert
Hi,

From your statements it is most likely the sequencer.



Sequencer # 621679 @ $35 + $6.75 shipping .


It can be seen and ordered from right side through PayPal here:

http://www.mobilehomerepair.com/NordyneElec.html



OR, by calling toll free between 9 and 5 CST week-days to

1-877-263-7860 and charging to Visa or Mastercard.


If in Canada, let us know for added info if ordering.



Thanks,
Robert