Furnace is cold.What parts do I need?

Posted: Fri Nov 09, 2007 8:14 am
by mrgbhunt
Let me start with type.It is an Evcon EB15A.Have checked the coils and have continuity throughout.I an at a loss since this is a home I purchased in April 2007 and didn't need heat till now.Could it be a sequencer or limit switch or possibly a thermostat problem since it was changed right after moving in.The blower runs.The air works.Just no heat.Where should I start.I can send pictures if needed.

Posted: Fri Nov 09, 2007 2:57 pm
by hvac1000
Could be thermostat not wired corectly
Could be sequencer
Could be circuit breakers in your main panel or on the furnace
Could be a limit switch.
There are many items that can cause no heat.

Is this a new home?
Is it under warrenty?
Do you have a electric meter and know how to use it?

RE: Furnace is cold.What parts do I need?

Posted: Fri Nov 09, 2007 3:56 pm
by mrgbhunt
Stat wired correctly,not sequencer,not breakers,not a new home,no warranty and yes I have a meter and know how to use one.

RE: Furnace is cold.What parts do I need?

Posted: Fri Nov 09, 2007 5:04 pm
by hvac1000
Simple just start following the voltage feed back from the elements until you find the device that is not functional and blocking current flow.

RE: Furnace is cold.What parts do I need?

Posted: Sat Nov 10, 2007 8:04 am
by Robert
Hi,


Did you test sequencer ?

Does blower motor come on in heat/auto mode ?


Or, does blower just work for a/c-auto mode ?


If you tested sequencer, how and what readings did you get ?




Thanks,
Robert

Re: RE: Furnace is cold.What parts do I need?

Posted: Sat Nov 10, 2007 8:56 am
by mrgbhunt
Robert wrote:Hi,


Did you test sequencer ?

Does blower motor come on in heat/auto mode ?


Or, does blower just work for a/c-auto mode ?

Thanks,
Robert
If you tested sequencer, how and what readings did you get ?

I tested sequencer and was getting 10V on H1/H2, H3/H4 and 240 on M1/M2,M3/M4,M5/M6.I have replaced the sequencer and think the trans output is low so am going to replace it.Blower motor comes on in heat auto mode.I am at a loss here since I have no schematics for this unit and don't know anything about it.I can send pictures if needed.

RE: Furnace is cold.What parts do I need?

Posted: Sat Nov 10, 2007 10:03 am
by Robert
You can order a wiring/parts diagram here after 9AM M - F:

http://www.mobilehomerepair.com/wireandparts.html




I wouldn't buy anymore parts until sure of problem as that could get costly unnecessarily.


For a $20 fee, I can offer one on one email help with unit.


http://www.mobilehomerepair.com/Order4b.html


IF you then purchase parts from us, we apply half of that to your parts order.



Thanks,
Robert