Model # DGRT070AUA
We recently replaced the blower motor on our furnace and now the blower works on continuous but not on Automatic. This was happening before the blower was changed as well but was accomplanied by the motor randomly shutting itself off. When on auto, when the thermostat is turned up, the burner turns on but the blower does not. What needs to be replaced now?
Coleman Evcon Presidential Gas Furnace Problem
Here is the part
7975-3281 Fan Switch
Here is where to order
http://www.mobilehomerepair.com/ColemanGas.html
left side half way down page.
7975-3281 Fan Switch
Here is where to order
http://www.mobilehomerepair.com/ColemanGas.html
left side half way down page.
God, grant me the serenity
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
thanks will order the part asap. one question though...where is the fan switch located on the furnace? sometimes the blower and the burner go on at the same time but do not turn off when on auto. the burner runs for a long period of time and turns off but the blower stays on.
Look for the disc that has this range on it.
CLOSE 110° OPEN 90°
Look in the box that is on the front of the furnace behind the furnace door.
Inside the box will be a transformer and some relays.
You will find two disc's that will look like what you ordered
According to what I can tell the disc on the left will be the one you want to replace. Just double check the open close numbers I gave you.
If you have a question once you get the part post back.
CLOSE 110° OPEN 90°
Look in the box that is on the front of the furnace behind the furnace door.
Inside the box will be a transformer and some relays.
You will find two disc's that will look like what you ordered
According to what I can tell the disc on the left will be the one you want to replace. Just double check the open close numbers I gave you.
If you have a question once you get the part post back.
God, grant me the serenity
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
thanks both of you for your help the numbers robert said are right and the part is right thanks guys i will order this from you guys asap and will post again if more help is needed or prob is still there
the fan switch worked great. the fan is doing what its supposed to now. however, for some reason we only have heat through one side of the house. the left side of the house is getting too much heat and the right side is getting barely any heat. the right side of the house is way too cold and the left side is like a sauna. all the ducts are connected. we are getting air through the vents just very little. any help would be greatly appreciated.
Probably just one, but may be two.
Go underneath home and look for large flex duct hanging down below underbelly.
It should be connected under the furnace and stretched across to connect to other side trunkline.
They get torn, kinked, come loose, etc. and no air gets to other side.
Best to replace with two 90* metal elbows and metal duct across.
Or, the two 90* ells and flex duct stretched tight between them.
Stops alot of problems this way.
Thanks,
Robert
Go underneath home and look for large flex duct hanging down below underbelly.
It should be connected under the furnace and stretched across to connect to other side trunkline.
They get torn, kinked, come loose, etc. and no air gets to other side.
Best to replace with two 90* metal elbows and metal duct across.
Or, the two 90* ells and flex duct stretched tight between them.
Stops alot of problems this way.
Thanks,
Robert
Last edited by Robert on Mon Dec 10, 2007 2:54 am, edited 1 time in total.
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
k thanks again robert i helped someone else in other topic fix air filter gave her both part numbers also i will go under in the morning tommarow already 3:19am here well im off to bed talk to you tomarrow robert
Hi,
You're very welcome.
Yep, me too. Burning midnight oil trying to catch up on the forum questions.
Eyelids getting very heavy,LOL.
Take care and best wishes,
Robert
You're very welcome.
Yep, me too. Burning midnight oil trying to catch up on the forum questions.
Eyelids getting very heavy,LOL.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
thx worked great heat comes out all vents right now house is warm on both sides what had happend is i went down to look for the big flex duct coming out of under belly and the big flex duct was held up by a big zip tie and some duct tape lol fell down new zip tie andduct tap its all better now thx again for all your loads of help
-
- Similar Topics
- Replies
- Views
- Last post
-
-
LOUD Blower on Coleman Presidential 2 900759
by AuntKatie » Thu Apr 05, 2018 6:50 pm » in Coleman Service & Repair - 0 Replies
- 44830 Views
-
Last post by AuntKatie
Thu Apr 05, 2018 6:50 pm
-
-
-
Colman evcon presidental 7980B856 furnace will not stay on
by ezridersid » Sat Dec 21, 2019 8:52 pm » in Mobile Home Repair - 1 Replies
- 17306 Views
-
Last post by ezridersid
Sat Dec 21, 2019 9:04 pm
-
-
- 0 Replies
- 110046 Views
-
Last post by cwwhite75
Sat Feb 29, 2020 8:46 am
-
-
I am thinking of switching to a gas water heater
by deryk the gypsy » Sat Jul 22, 2017 7:16 am » in Mobile Home Repair - 2 Replies
- 39159 Views
-
Last post by Greg
Sat Jul 22, 2017 12:26 pm
-
-
-
Need to remove a stripped Allen wrench-type plug from the OUT PRESS port on top of gas valve
by justplumducky » Fri Aug 25, 2017 8:21 am » in Nordyne Service & Repair - 1 Replies
- 49079 Views
-
Last post by Maxwell.lipphardt
Mon Feb 04, 2019 6:29 am
-