The mobile home I just purchased has the Nordyne E2EB-015HA unit and just replaced the main breaker to get it to work. The unit was heatig very well untill last night. The air temp coming out of the vent was room temp. No heat at all. I checked the power coming in and all is good on both breakers, in and out. I dont kow much about HVAC so ay help wood be very apreciated.

Thanks

RE: Nordyne E2EB-015HA not heating

Posted: Wed Nov 14, 2007 1:19 am
by Robert
Hi,

On an electric furnace, the sequencer controls the heating elements and the blower motor.


For blower motor to be running, you should have at least one element energized.


Can you see if any elements are energized or any heat being generated around element compartment ?


Most likely a faulty sequencer.