Fixing sections of duct that connect floor vent to main line
Posted: Tue Dec 18, 2007 9:25 pm
by cgfilter
What are my options on repairing the sections of ductwork that connect the floor vents to the main trunk line? i have the aluminum duct, not flex. I'm tired of losing so much of my heated, or cooled air to the the outside. Thanks in advance!
casey...
RE: Fixing sections of duct that connect floor vent to main
Posted: Wed Dec 19, 2007 3:08 am
by Robert
Hi Casey,
Are you in a single, double or triple ?
Are the registers over the trunkline or away from it ?
Thanks,
Robert
RE: Fixing sections of duct that connect floor vent to main
Posted: Wed Dec 19, 2007 11:06 am
by cgfilter
sorry, i should have given more info. anyway, i'm in single wide where all the floor vents are inline with, and come straight up from the main trunk line.
RE: Fixing sections of duct that connect floor vent to main
Posted: Fri Dec 21, 2007 4:40 am
by Robert
Hi Casey,
Get some aluminum flashing and attach to whats there with sheet metal screws.
This should cover any gaps/holes where it has come loose or opened.
Then cover all seams with foil backed tape.
Take care and best wishes,
Robert