Intertherm problem

Posted: Fri Feb 01, 2008 6:18 am
by johnrock11j
Intertherm model #687133. The combustion motor kicks on and then the furnace clicks on and off several times before it will kick on. I can see the ignitor start glowing and the it quits. Sometimes it will do this several times before finally lighting. Thanks for any help. :?

RE: Intertherm problem

Posted: Fri Feb 01, 2008 6:41 am
by Robert
What is the furnace model number ?


Thanks,
Robert

RE: Intertherm problem

Posted: Fri Feb 01, 2008 7:47 am
by johnrock11j
It's an M1 SERIES

RE: Intertherm problem

Posted: Fri Feb 01, 2008 10:29 am
by Robert
Need complete number, there are a few variations in the M1 series.



Thanks,
Robert

RE: Intertherm problem

Posted: Fri Feb 01, 2008 5:29 pm
by johnrock11j
Model # M1MB 070A BW
SERIAL # M1M98 100 1373
If neither one of these are It could you tell me where to find It. Sorry and thank you.

RE: Intertherm problem

Posted: Sat Feb 02, 2008 12:52 am
by Robert
Hi,

The furnace has a control board with two diagnostic bulbs, one red and one yellow.


What is status of each, solid, not lit, flashing, etc... ?


If flashing, how many blinks each sequence ?



Thanks,
Robert

RE: Intertherm problem

Posted: Sat Feb 02, 2008 9:02 am
by johnrock11j
Sometimes It flashes sometimes It doesn't. When It does It flashes twice (Open Pressure switch). I replaced the two pieces of tubing awhile back and It seemed to fix It but It still acts up occasionally. It doesn't do this all the time some times It takes right off and works fine. Thank you

RE: Intertherm problem

Posted: Sat Feb 02, 2008 3:47 pm
by Robert
Hi,

You have an air pipe coming into the booster motor. It has to be clear and undamaged.

Then the motor/wheel has to be undamaged and running fine.

Then the tubes have to be clear/unclogged, attached tightly with no tears or damage.


Then the pressure switch has to be operable and have 24-28vac coming to it.


On a call for heat from t-stat, booster motor should start immediately.

It will pull air in through air pipe, through wheel and out through tubes and pressure switch.


When a preset water column pressure is reached, the pressure switch contacts close sending the 24-28vac signal on to energize furnace components.

If everything except pressure switch seems/is ok and the pressure switch has 24-28vac input, then the switch is probably going bad.


If you would like ordering info or price quote, let me know.



Thanks,
Robert

RE: Intertherm problem

Posted: Sun Feb 03, 2008 10:03 am
by johnrock11j
I would like ordering info and price quote. Thank you Robert.

RE: Intertherm problem

Posted: Mon Feb 04, 2008 12:26 am
by Robert
Hi John,


You're very welcome, happy to help.

Pressure Switch # 632453 @ $27.42 + $6.75 shipping .

It is the new replacement number for old # 632332.


You can see and order it through PayPal from right side here:

http://www.mobilehomerepair.com/NordyneGas.html


Or, by calling toll free after 9AM CST to 1-877-263-7860

and charging to Visa or Mastercard.


Let me know if you're outside the U.S. for added ordering info.


Thanks.



Take care and best wishes,
Robert