I have a question about instalation of a thermostat.
First off I have yet to find the exact model number on the furnance but is a 17Kw unit in the EB series I believe. This unit was taken out of a mobel home and is now being used to heat a office area. This is being used for heat only and not connecting in to any AC unit.
The wires were never marked on the thermostat when removed so not sure which control what. I have 4 Wires red, green, black, white that come out.
I purchased a Hunter 40020A manual thermostat for heating system only. This unit ony has place for 2 wire; a W and RH area. I currently have the White in the W and Red in the RH area with the green and black leading no where. Thermostat does activate. Blower turns on and then warm air moves out. I have about 95 degree air coming out right into the box at teh heating coils. Is this sound about right or is only one stage of heating unit working? I have let run for about 1 hour intervals and no build up of higher tempatures. Is there a way of testing which elements are on with a volt meter? Can this 2 wire system be used or do I need one for heat/cooling still? If can be used, which 2 wires need to be connected if not connected right?
any help with this would be great.
Wiring up thermostat
Hi,
Red to RH and White to W is correct.
Red = 24volt power to t-stat
White= Heat wire back to furnace
Black= Common wire to outside a/c condenser (not needed)
Green= Blower motor wire back to furnace for a/c mode and fan continous on. (not needed)
Do you have a Fan auto/on switch at furnace ? If so, set it to auto.
Set it to ON if you ever want continous fan.
Your model number will be on a sticker on front facing of furnace, usually midway or down low.
You can test for voltage at each element by placing a meter lead on each side connection point for each element, should read 240VAC.
If not, check sequencer. Should have 24-28VAC at very bottom terminals front to back.
If you have that on both seq. stacks, then need to check top and middle terminals for resistance.
Turn power off, mark where wires go and remove wires from M1/M2, M3/M4 and M5/M6 and tape all ends good with elect. tape.
Then turn power on and retest bottom for 24-28vac. If there with call for heat from t-stat, then ohm the above sets of M terminals to see if they show resistance/continuity.
If not, the sequencer is bad.
Sequencer # 3115-3571 can be seen and ordered through PayPal
from right side here if needed:
http://www.mobilehomerepair.com/ColemanElec.html
Thanks for inquiring.
Take care and best wishes,
Robert
Red to RH and White to W is correct.
Red = 24volt power to t-stat
White= Heat wire back to furnace
Black= Common wire to outside a/c condenser (not needed)
Green= Blower motor wire back to furnace for a/c mode and fan continous on. (not needed)
Do you have a Fan auto/on switch at furnace ? If so, set it to auto.
Set it to ON if you ever want continous fan.
Your model number will be on a sticker on front facing of furnace, usually midway or down low.
You can test for voltage at each element by placing a meter lead on each side connection point for each element, should read 240VAC.
If not, check sequencer. Should have 24-28VAC at very bottom terminals front to back.
If you have that on both seq. stacks, then need to check top and middle terminals for resistance.
Turn power off, mark where wires go and remove wires from M1/M2, M3/M4 and M5/M6 and tape all ends good with elect. tape.
Then turn power on and retest bottom for 24-28vac. If there with call for heat from t-stat, then ohm the above sets of M terminals to see if they show resistance/continuity.
If not, the sequencer is bad.
Sequencer # 3115-3571 can be seen and ordered through PayPal
from right side here if needed:
http://www.mobilehomerepair.com/ColemanElec.html
Thanks for inquiring.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 65441 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-
-
- 4 Replies
- 32396 Views
-
Last post by Greg
Mon Apr 16, 2018 4:20 pm
-
- 5 Replies
- 56020 Views
-
Last post by mdnagel
Sat Jun 29, 2019 8:09 pm
-
- 0 Replies
- 43206 Views
-
Last post by biddlefam
Sun Nov 10, 2019 11:17 am
-
-
I need wiring assistance for a miller furnace serial number A0981-0685
by Timodell » Wed Nov 20, 2019 10:40 pm » in Nordyne Service & Repair - 0 Replies
- 65703 Views
-
Last post by Timodell
Wed Nov 20, 2019 10:40 pm
-