Posted: Wed Mar 05, 2008 8:25 pm
by Guest
hi, i installed a heat pump on a gas furance using a fossil fuel kit.it has been working fine till today . now when it goes into defrost the furance doesnt lite and of course it blows cold air until defrost is over any thoughts thanks,electricman

RE: coleman gas furance with heat pump

Posted: Thu Mar 06, 2008 12:17 am
by Robert
Hi,


Look at wiring diagram for units including the fossil fuel kit and trace circuit from HP during defrost back to furnace.


Sounds like a loose wire or loss of low voltage circuit back to gas valve.


Tracing wires from gas valve backwards could point to it as it is somewhere between the short distances from one to the other.



Take care and best wishes,
Robert

RE: coleman gas furance with heat pump

Posted: Thu Mar 06, 2008 8:17 pm
by Guest
thanks robert for your reply, when checked the unit today it was working ok. so i guess you must be right mabey a losse wire i will let you know when and if it does it again. thanks again i havent been in this line of work very long but thanks to guys like you i am learning sometimes the hard way lol. THANKS AGAIN ,electricman

RE: coleman gas furance with heat pump

Posted: Fri Mar 07, 2008 3:53 am
by Robert
Hi,

I remember those days still and occassionally still have them after 28+ years. It is a very rewarding, but very demanding and ever changing trade, so learning will always be a present thought.


Let me know when it hiccups again. Running fingers along wires slightly wiggling them will sometimes locate the problem, but check all connections first.



Take care and best wishes,