AC unit outside not turning on
The blower inside is working fine but the outside unit isn't turning on. I checked the wires that connect and it doesn't look like there's any break in them. What else should I look for? I'm obviously trying to save money and not have to hire someone to fix it unless I really have to.
Is NOTHING coming on outside, no compressor or fan motor ?
If that's the case, turn power off and remove controls panel cover.
May be a bad contactor.
FIRST though, go to t-stat and turn t-stat off, then test across R or RC and Y for 24-28vac.
If you have it, turn t-stat on and set to cool-auto-65* and test across same R or Rc and Y for 24vac.
Should read 0vac.
Let me know.
Thanks,
Robert
If that's the case, turn power off and remove controls panel cover.
May be a bad contactor.
FIRST though, go to t-stat and turn t-stat off, then test across R or RC and Y for 24-28vac.
If you have it, turn t-stat on and set to cool-auto-65* and test across same R or Rc and Y for 24vac.
Should read 0vac.
Let me know.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
i am having the same problem but the contactor is pulling in and humming. i tested the thermostat as you said and it is fine.
Hi,
Test across the two small wires connected at sides of contactor for 24-28vac.
IF there, test at top two large wires for 240vac and at bottom two large wires for 240vac.
Look for incoming wires into condensing unit and going to eitehr bottom or top.
Then the other end of contactor goes to compressor.
IF you have 240vac at both ends, see if you have only ONE Run Capacitor, if so, it is a dual run cap and may be bad.
Reply back in a new thread to not confuse with this one.
Thanks,
Robert
Test across the two small wires connected at sides of contactor for 24-28vac.
IF there, test at top two large wires for 240vac and at bottom two large wires for 240vac.
Look for incoming wires into condensing unit and going to eitehr bottom or top.
Then the other end of contactor goes to compressor.
IF you have 240vac at both ends, see if you have only ONE Run Capacitor, if so, it is a dual run cap and may be bad.
Reply back in a new thread to not confuse with this one.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 116439 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167385 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
- 3 Replies
- 37367 Views
-
Last post by David DeBord
Sun Oct 22, 2017 8:16 am
-
- 15 Replies
- 110678 Views
-
Last post by Greg
Tue Mar 19, 2019 5:32 pm
-
- 2 Replies
- 25980 Views
-
Last post by Mark440
Tue Mar 03, 2020 8:35 pm