No ignition, bad control board?
Posted: Mon Apr 14, 2008 7:20 pm
I woke up one morning to a horrendous noise from my furnace. It turns out that the fan inside the combustion blower broke apart (it was plastic). I replaced it with a new fan assembly made of steel. Seems to be getting good suction...I check for air flow on the outside vent.
The problem now is the igniter element is not heating up. The control board is blinking 3 flashes - which decodes to pressure switch stuck open. When I suck on the combustion side of the switch briefly the heating element will glow and eventually the gas comes on. So, I thought I had a bad pressure switch. I just ordered a new pressure switch, and no luck. Still 3 blinking lights and no heat.
I tested to see if the pressure switch was getting any voltage from the control board and nothing. Could it be the control board? I just wanted to see if that may sound to be the culprit, as the control board is not a 25$ part![Smile :)](./images/smilies/icon_smile.gif)
ps. model number: P3URD12N07501A
The problem now is the igniter element is not heating up. The control board is blinking 3 flashes - which decodes to pressure switch stuck open. When I suck on the combustion side of the switch briefly the heating element will glow and eventually the gas comes on. So, I thought I had a bad pressure switch. I just ordered a new pressure switch, and no luck. Still 3 blinking lights and no heat.
I tested to see if the pressure switch was getting any voltage from the control board and nothing. Could it be the control board? I just wanted to see if that may sound to be the culprit, as the control board is not a 25$ part