Wondering if you could help me out, I have a DGAA Coleman series furnace in a single wide home.
My problem is that when the thermostat is turned to cool the circuit board fuse blows, but when turned to heat the furnace starts and runs fine. The ac worked last year but the air from the vents was only 15 degrees celsius. This year it wont even turn on.
I'm thinking a short somewhere, so I disconected the two leads from the board out to the condenser unit but the fuse still blew so its not on that line, Any other ideas? Can the board fail internally, I checked and found no signs of scorched board or fried electronics. Any help is appreciated.
Mrdman2442@Yahoo.ca
AC issue
Hi,
First trace all wires in 24vac low voltage circuit. and look for any bare spots, especially at entrances to unit.
At t-stat, turn power OFF, remove Red, Yellow and Green wires and tie/tape together. Then restore power and see what happens.
IF it still blows fuse, transformer and board and wires to/from each is all that's left.
Then if nothing found, you'll have to isolate each component until you locate the short.
Thanks for inquiring,
Robert
First trace all wires in 24vac low voltage circuit. and look for any bare spots, especially at entrances to unit.
At t-stat, turn power OFF, remove Red, Yellow and Green wires and tie/tape together. Then restore power and see what happens.
IF it still blows fuse, transformer and board and wires to/from each is all that's left.
Then if nothing found, you'll have to isolate each component until you locate the short.
Thanks for inquiring,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
DGAT Series furnace air-conditioning issue
by minnie1967 » Thu Jul 13, 2017 9:48 am » in Coleman Service & Repair - 0 Replies
- 61983 Views
-
Last post by minnie1967
Thu Jul 13, 2017 9:48 am
-
-
-
1989 Champion, entrance door issue, need advice
by hotrod53 » Mon Dec 30, 2019 5:33 pm » in Mobile Home Repair - 3 Replies
- 47602 Views
-
Last post by Greg
Tue Dec 31, 2019 7:27 pm
-
-
-
Nordyne M1B1 furnace issue - thermostat c wire not hooked up correctly. It's running off atteries instead
by Tallestt » Mon Apr 20, 2020 6:27 am » in Nordyne Service & Repair - 1 Replies
- 43413 Views
-
Last post by taurolyon
Tue Jun 23, 2020 4:02 pm
-
-
-
Nordyne model m1mb 070a bw power issue
by Combustibleink » Mon Nov 16, 2020 10:21 am » in Nordyne Service & Repair - 0 Replies
- 116191 Views
-
Last post by Combustibleink
Mon Nov 16, 2020 10:21 am
-
-
- 0 Replies
- 119334 Views
-
Last post by mobtek
Fri Mar 26, 2021 10:30 am