ac wont turn off
Its a presidential 3 model 7956A856. AC unit and blower runs constantly regardless off tstat setting. We flipped the switch to cool and it never shuts off unless you flip to heat or shut off the main power. Replaced blower relay and sequencer and tested with 2 tstats. Heat side works fine. Even with the tstat wires at the furnace disconnected it still runs. Any help would be appreciated. thanks
Hi,
IF you only have 2 wires connected at t-stat, it is probably a stuck t-stat reversing relay inside the a/c control box.
Thanks,
Robert
IF you only have 2 wires connected at t-stat, it is probably a stuck t-stat reversing relay inside the a/c control box.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I am not too familiar with furnace setups but the sequencer should be the reversing relay right, and I have already replaced that. I have 26.5 volts going to the ac unit regardless of tstat setting and the ac unit relay is working properly with voltage on without voltage off. But even with the wires disconnect that run to the ac unit disconected the blower still runs. So I am sure the problem is at the furnace, but am really out of ideas.
Sometimes a sequencer is used as the reversing relay.
If all components seem ok, check wires for bare spots allowing them to touch creating a short circuit.
Thanks,
Robert
If all components seem ok, check wires for bare spots allowing them to touch creating a short circuit.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167495 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
In too deep to turn back now... now what?
by Do it herselfer » Thu Nov 02, 2017 11:28 pm » in Mobile Home Repair - 2 Replies
- 26401 Views
-
Last post by yakima4$
Tue Dec 05, 2017 8:29 pm
-
-
-
3500A816 Randomly wont start or shut down
by Smithcraft » Fri Jan 13, 2023 4:04 pm » in Coleman Service & Repair - 0 Replies
- 95205 Views
-
Last post by Smithcraft
Fri Jan 13, 2023 4:04 pm
-
-
- 1 Replies
- 42054 Views
-
Last post by Greg
Sat Jan 06, 2018 9:11 am
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 116536 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-