Red T (Coleman) Model # DLAS075ADC - Need Help
I need some help with my furnace. Everything seems to be working except for the blower doesn't start. I can set the thermostat and it kicks the unit on, but the upper limit switch gets thrown before the blower starts. Please give me some advice and where to start looking for the problem. Thx, Nick. ![Shocked :shock:](./images/smilies/icon_eek.gif)
![Shocked :shock:](./images/smilies/icon_eek.gif)
Hi Nick,
Disconnect the blower motor leads and test to see if you have full 120vac at the plug or connection.
If not, need to find interruption of circuit.
If you do, spin the blower wheel CAREFULLY with a call for heat and see if the motor starts.
If it does with a spin, probably need a new run capacitor.
If not and it has full 120vac power to it, need a new motor and run cap.
Can also order a wiring diagram if needed and/or pay a $20 troubleshooting fee for email instructions on things to test in circuit.
Thanks,
Robert
Disconnect the blower motor leads and test to see if you have full 120vac at the plug or connection.
If not, need to find interruption of circuit.
If you do, spin the blower wheel CAREFULLY with a call for heat and see if the motor starts.
If it does with a spin, probably need a new run capacitor.
If not and it has full 120vac power to it, need a new motor and run cap.
Can also order a wiring diagram if needed and/or pay a $20 troubleshooting fee for email instructions on things to test in circuit.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
![Cool 8)](./images/smilies/icon_cool.gif)
Thanks again for your help. I do home security (tech), so if you ever have any security questions, please shoot me a line, I would be more than happy to return the favor. Thanks again. Nick.
Hi Nick,
Sounds good, thanks for update. Sometimes the run cap alone won't do it, but often does when motor starts and runs with a spin of wheel.
Since the run cap must be replaced with a new motor, always best to try the spin move and run cap first.
Thanks for the security help offer, I'll keep ya in mind for future help if ever needed.
Take care and best wishes,
Robert
Sounds good, thanks for update. Sometimes the run cap alone won't do it, but often does when motor starts and runs with a spin of wheel.
Since the run cap must be replaced with a new motor, always best to try the spin move and run cap first.
Thanks for the security help offer, I'll keep ya in mind for future help if ever needed.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Need help identifying manufacturer of back door
by nestsman » Mon Oct 09, 2017 11:25 am » in Mobile Home Repair - 2 Replies
- 22965 Views
-
Last post by UmpJJ
Wed Oct 18, 2017 8:48 am
-
-
-
Home is shifting and sinking - Need help!
by Catherine405 » Tue May 29, 2018 1:35 pm » in Mobile Home Repair - 3 Replies
- 11597 Views
-
Last post by Greg
Wed May 30, 2018 7:58 pm
-
-
- 5 Replies
- 16083 Views
-
Last post by Greg
Thu Oct 18, 2018 7:38 pm
-
-
Sagging floor under toilet, need help with size of shutoff fittings
by ferret13sj » Thu Nov 17, 2022 9:37 pm » in Mobile Home Repair - 4 Replies
- 63434 Views
-
Last post by yakima4$
Thu Dec 01, 2022 11:16 pm
-
-
-
Eb12eb Coleman furnace 4 speed help.
by Johnwayne892000 » Thu Aug 30, 2018 7:37 pm » in Coleman Service & Repair - 0 Replies
- 25027 Views
-
Last post by Johnwayne892000
Thu Aug 30, 2018 7:37 pm
-