WE have a coleman 7970C856 Presidential Evcon model.. Not sure if it should be a o as in number or O as in letter after the 2nd 7..
But anyways our furnance will run for awhile then shut off then about a minute later it kicks right back on again and runs for awhile again.. then is good for about 15-20 minutes like it should be then it does it again..
Any ideas?? Thermastat?
The repairman was here and fixed a orphis and got the pilot light back like it should be etc etc.. but just made up some bs on the heat exchanger does that sometimes etc etc...
Coleman 797oc856
Hi,
All numbers except for the letter C, 7970C856 .
Does the burner go out with the blower motor or just the blower motor ?
Thanks,
Robert
All numbers except for the letter C, 7970C856 .
Does the burner go out with the blower motor or just the blower motor ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
The blower shuts off then it makes that rumbling noise like it does after it ignites the first time.. does that for awhile and kicks on again and runs for awhile
Blower issue?? Also some times it makes a humming noise you can hear.. Thats not all the time though
Blower issue?? Also some times it makes a humming noise you can hear.. Thats not all the time though
Hi,
Could be the blower shutting down, which would cause the limit to shut down burner.
Then starting up again.
May be a fan switch bad for example. Would need to test circuits for voltage to know what is happening for sure.
Take care and best wishes,
Robert
Could be the blower shutting down, which would cause the limit to shut down burner.
Then starting up again.
May be a fan switch bad for example. Would need to test circuits for voltage to know what is happening for sure.
Take care and best wishes,
Robert
Last edited by Robert on Sat Oct 04, 2008 8:33 am, edited 1 time in total.
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I see the fan switches are pretty cheap..
Can i replace one?? Seems like it just plugs in
we had a old one laying around.. I think we replaced one years ago..
Are these common to go every 5-7 years??
Do you have one for my model furnance??
I pulled these numbers off the switch
7660-326 it says fan switch below
F110-20F
20050060T82
9225
Can i replace one?? Seems like it just plugs in
we had a old one laying around.. I think we replaced one years ago..
Are these common to go every 5-7 years??
Do you have one for my model furnance??
I pulled these numbers off the switch
7660-326 it says fan switch below
F110-20F
20050060T82
9225
Hi,
That could be the problem as it is common every 5-10 years to have one act up due to weakened contacts.
Fan Switch # 7975-3281 can be seen and ordered through PayPal from left side of page here :
http://www.mobilehomerepair.com/ColemanGas.html
Take care and best wishes,
Robert
That could be the problem as it is common every 5-10 years to have one act up due to weakened contacts.
Fan Switch # 7975-3281 can be seen and ordered through PayPal from left side of page here :
http://www.mobilehomerepair.com/ColemanGas.html
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 0 Replies
- 57602 Views
-
Last post by Montanan
Wed Jan 03, 2018 1:03 pm
-
- 0 Replies
- 50148 Views
-
Last post by Kourgath
Fri Mar 23, 2018 3:41 pm
-
-
LOUD Blower on Coleman Presidential 2 900759
by AuntKatie » Thu Apr 05, 2018 6:50 pm » in Coleman Service & Repair - 0 Replies
- 44867 Views
-
Last post by AuntKatie
Thu Apr 05, 2018 6:50 pm
-
-
-
Eb12eb Coleman furnace 4 speed help.
by Johnwayne892000 » Thu Aug 30, 2018 7:37 pm » in Coleman Service & Repair - 0 Replies
- 25013 Views
-
Last post by Johnwayne892000
Thu Aug 30, 2018 7:37 pm
-
-
-
Coleman 6806a furnace doesn't stop heating even with tstat disconnected. Any ideas?
by Neighbor Bill » Mon Dec 31, 2018 1:01 pm » in Coleman Service & Repair - 1 Replies
- 41738 Views
-
Last post by Neighbor Bill
Mon Dec 31, 2018 1:06 pm
-