My daughter has a Coleman Evcon DGAT056BDC furnace in her modular home. She had a lighting strike that knocked out her PC monitor and DVD player earlier this summer.
She tried to fire the furnace up last night and it wouldn't light. I went over to look @ it today. The combustion fan started fine, I could see the ignitor glow, but no flame. I put a meter on the 2 leads to the gas valve and am not getting any voltage, AC or DC, to it . Would this lead you to believe the ignition controller is no good ?? Its a Robertshaw HS780-34NR-306A.
Thanks
Coleman Evcon DGAT056BDO
Hi,
When ignitor glows, it glows for approx. 35 seconds. Then the Valve terminal on ignition module should energize the gas valve for 6 seconds.
Start the call for heat, let booster motor run, centrifugal switch closes sending 24vac to TH terminal on module.
TH to GRND = 24vac
After 15 second purge cycle,Ignitor glows, watch for approx. 35 seconds, then see if module sends 24vac to gas valve for 6 seconds.
VALVE to GRND = 24vac.
IF all is ok up to the 24vac going to gas valve and that does not happen, module is bad.
Again, if you get 24vac across TH and GRND, but do not get 24vac across VALVE and GRND at appropriate timings, module is bad.
Ignition Module # 1474-0061/A can be seen and ordered through PayPal if needed from right side of page here :
http://www.mobilehomerepair.com/ColemanGas.html
Take care and best wishes,
Robert
When ignitor glows, it glows for approx. 35 seconds. Then the Valve terminal on ignition module should energize the gas valve for 6 seconds.
Start the call for heat, let booster motor run, centrifugal switch closes sending 24vac to TH terminal on module.
TH to GRND = 24vac
After 15 second purge cycle,Ignitor glows, watch for approx. 35 seconds, then see if module sends 24vac to gas valve for 6 seconds.
VALVE to GRND = 24vac.
IF all is ok up to the 24vac going to gas valve and that does not happen, module is bad.
Again, if you get 24vac across TH and GRND, but do not get 24vac across VALVE and GRND at appropriate timings, module is bad.
Ignition Module # 1474-0061/A can be seen and ordered through PayPal if needed from right side of page here :
http://www.mobilehomerepair.com/ColemanGas.html
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Concerning your comment in this area.....
"Again, if you get 24vac across TH and GRND, but do not get 24vac across VALVE and GRND at appropriate timings, module is bad."
I have the electronic ignition module with the EVCON 1474-004 that lights, fires and intermittantly shuts valve off during run cycle.
I have monitored the TH side and maintain 24-26 volts even during shutoff.
But when monitoring the valve terminal of the ignitor-- it drops to zero when the valve shuts off.
Again TH side never drops.
Does this intermittant drop mean the ignitor is bad....?
or could it be something else?
The fan blower is up and running....
and exhaust fan shuts on once the valve closes.
Anything you can offer? It seems my unit eats ignitors .
I have replaced 3 in 19 years.
"Again, if you get 24vac across TH and GRND, but do not get 24vac across VALVE and GRND at appropriate timings, module is bad."
I have the electronic ignition module with the EVCON 1474-004 that lights, fires and intermittantly shuts valve off during run cycle.
I have monitored the TH side and maintain 24-26 volts even during shutoff.
But when monitoring the valve terminal of the ignitor-- it drops to zero when the valve shuts off.
Again TH side never drops.
Does this intermittant drop mean the ignitor is bad....?
or could it be something else?
The fan blower is up and running....
and exhaust fan shuts on once the valve closes.
Anything you can offer? It seems my unit eats ignitors .
I have replaced 3 in 19 years.
Hi,
Please post your questions in a new thread. We keep each thread to original poster to keep down confusion in following the questions and answers.
Thanks,
Robert
Please post your questions in a new thread. We keep each thread to original poster to keep down confusion in following the questions and answers.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 0 Replies
- 110103 Views
-
Last post by cwwhite75
Sat Feb 29, 2020 8:46 am
-
-
Colman evcon presidental 7980B856 furnace will not stay on
by ezridersid » Sat Dec 21, 2019 8:52 pm » in Mobile Home Repair - 1 Replies
- 17314 Views
-
Last post by ezridersid
Sat Dec 21, 2019 9:04 pm
-
-
-
Transformer burning out in an Evcon DES 80
by BigDave67s » Wed Dec 29, 2021 10:01 pm » in Coleman Service & Repair - 0 Replies
- 112048 Views
-
Last post by BigDave67s
Wed Dec 29, 2021 10:01 pm
-
-
-
Evcon Heat Pump - Air Conditioner Model No. BRHS036B Making HUM Before Starting
by Dave_L » Tue Aug 29, 2023 1:26 am » in Coleman Service & Repair - 0 Replies
- 126602 Views
-
Last post by Dave_L
Tue Aug 29, 2023 1:26 am
-
-
- 0 Replies
- 57616 Views
-
Last post by Montanan
Wed Jan 03, 2018 1:03 pm