I'm having a strange problem with heat output from my Coleman Evcon EB15B. The short version is that it is only putting out about 80-degree air. I've checked the volts to all heater coils, as well as ohms through them. Upon initially turning on, it will put out 100-degree air, but will drop back to 80-degrees after a minute or so. Could it be the sequencer?
Any ideas would be greatly appreciated.
Lilly
Electric furnace not hot enough
If it runs does it heat the home? Electric heat does not get as hot a propane/oil heat so do not base you temperature discharge on a comparison basis. if all the heaters are working you are getting the maximum amount of heat the unit is capable of producing.
If you have a amprobe you can take the current draw (not voltage) of each heater to make sure they are all working.
hvac1000
If you have a amprobe you can take the current draw (not voltage) of each heater to make sure they are all working.
hvac1000
It does run, but last night the outside temperature was about 25 degrees, and the heater was running all the time and only kept the temperature inside at 68. The thermostat was set on 70. I have plans to check the amp draw on all legs of each heating element tonight, but I do not think any of the elements are bad, considering I know that it CAN put out 20-degree hotter air than it is now.
Lilly
Lilly
Check the elements. If they are good but not getting hot it is possible that the heat sequencer is defective. But before you condem the sequencer I would follow the voltage trail and make sure that no other safety device (limit control) is stopping the power on the way to the heaters. Remember you need 220 volts on each element. 110 volts on each side of the element and 220 volts across the element.
hvac1000
hvac1000
Check the limit switches for continuity. test one at at time. Remove wires and remember where you removed them from. Next check for continuity thru the limit to see if it is open or closed. They stop the flow of current when they are open. This is or limit switches.
hvac1000
hvac1000
IF you can get to the sequencer with enough room for testing voltage and feel comfortable doing so, test across M1/M2, M3/M4 and M5/M6 after waiting 2 minutes from call of heat by t-stat.
You should read 0 vac across all 3 sets and it should remain that way for a few minutes as home warms up.
You may have a set of contacts dropping out early, thus losing one or more elements.
Robert
You should read 0 vac across all 3 sets and it should remain that way for a few minutes as home warms up.
You may have a set of contacts dropping out early, thus losing one or more elements.
Robert
When it does not work and has zero amp draw, immediately test across Sequencer M5/M6 for 240vac.
Then test across both ends of bottom element for 240vac.
IF M5/M6 reads 0vac and the element reads 240vac, it's most likely a bad element.
If you get any readings other than this, it's a power/wiring problem.
Thanks,
Robert
Then test across both ends of bottom element for 240vac.
IF M5/M6 reads 0vac and the element reads 240vac, it's most likely a bad element.
If you get any readings other than this, it's a power/wiring problem.
Thanks,
Robert
Turn t-stat to OFF.
Then test across M5/M6 for 240vac .
IF you read 240vac, continue.
Turn t-stat to call for Heat.
Test across H3/H4 . Test for 24-28vac.
IF you read 24-28vac, continue.
Test across M5/M6 for 240vac.
IF you read 0vac, continue.
Test across the element terminals for 240vac.
BEFORE doing these, check and be sure ALL wires are connected tight and secure.
Check sequencer, element and limit connections.
Thanks,
Robert
Then test across M5/M6 for 240vac .
IF you read 240vac, continue.
Turn t-stat to call for Heat.
Test across H3/H4 . Test for 24-28vac.
IF you read 24-28vac, continue.
Test across M5/M6 for 240vac.
IF you read 0vac, continue.
Test across the element terminals for 240vac.
BEFORE doing these, check and be sure ALL wires are connected tight and secure.
Check sequencer, element and limit connections.
Thanks,
Robert
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 74891 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
- 4 Replies
- 9753 Views
-
Last post by Cherry_bomb
Thu Aug 17, 2017 11:28 am
-
- 2 Replies
- 27489 Views
-
Last post by plumducky
Tue Dec 10, 2019 3:59 pm
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167385 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
- 0 Replies
- 32624 Views
-
Last post by clsmatHH
Wed Oct 16, 2019 12:43 pm