Intertherm 900759 blower unit attached on top of a coleman 7956-856 furnace.
Came home yesterday to no A/C, no blower. Set thermostat to Off and fan to ON on the t-stat. Blower won't come on. Previously unit worked fine, no problems with the t-stat.
Have had the blower motor replaced about 2 years ago by a local outfit, who said they had a hard time finding a motor for it. Replaced unit was about 2x as loud as the original, so I'm suspicious of it already.
What troubleshooting plan do I follow to figure out which component is the problem. Is there a troubleshooting guide for this?
Thanks
Jeff
No blower again
Furnace : Coleman 7956-856
Blower above it : Intertherm 900759 (labeled Heating Cooling Blower)
External A/C heat exchanger : Intertherm Model # CNS50BCRAA 85MR04
Basically I see that the blower is comprised of a motor/fan, a large capacitor (for motor start I guess) and something in a rectangular box that looks like a florescent light ballast.
All the electrical wiring runs into a molded plastic plug into what appears to be a controller with a coleman 7900 label on it. So I suspect that is the thermostat unit.
Any troubleshooting tips welcome.
Jeff
Blower above it : Intertherm 900759 (labeled Heating Cooling Blower)
External A/C heat exchanger : Intertherm Model # CNS50BCRAA 85MR04
Basically I see that the blower is comprised of a motor/fan, a large capacitor (for motor start I guess) and something in a rectangular box that looks like a florescent light ballast.
All the electrical wiring runs into a molded plastic plug into what appears to be a controller with a coleman 7900 label on it. So I suspect that is the thermostat unit.
Any troubleshooting tips welcome.
Jeff
Hi Jeff,
Is the outside a/c condensing unit running with t-stat in Cool-Auto-65* mode ?
Does the rectangular metal box on front of blower housing have two rocker switches on front of it ?
Heat-Off-Cool and Fan-Auto are the two switches if applicable ?
Thanks,
Robert
Is the outside a/c condensing unit running with t-stat in Cool-Auto-65* mode ?
Does the rectangular metal box on front of blower housing have two rocker switches on front of it ?
Heat-Off-Cool and Fan-Auto are the two switches if applicable ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Jeff,
That's the a/c control box. Remove front cover and locate the transformer.
LINE - PRIMARY Side = 120vac
LOAD - SECONDARY Side = 24vac
Test it to see if you have power.
Thanks,
Robert
That's the a/c control box. Remove front cover and locate the transformer.
LINE - PRIMARY Side = 120vac
LOAD - SECONDARY Side = 24vac
Test it to see if you have power.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Jeff,
Yes, transformer is bad.
Transformer # 2940A3541 can be seen and ordered through
PayPal from left side of page here :
http://www.mobilehomerepair.com/ColemanGas.html
Go to auto parts store and get 3amp atc type plug in fuse and install in the power wire on 24vac secondary side of transformer.
Wrap with electrical tape.
It will protect it from low voltage shorts.
Thanks,
Robert
Yes, transformer is bad.
Transformer # 2940A3541 can be seen and ordered through
PayPal from left side of page here :
http://www.mobilehomerepair.com/ColemanGas.html
Go to auto parts store and get 3amp atc type plug in fuse and install in the power wire on 24vac secondary side of transformer.
Wrap with electrical tape.
It will protect it from low voltage shorts.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Finally got back to fixing this. Problem is that the transformer in the control box has 6 tabs while the one you recommended has 4.
I know 2 are line, 2 are load, and I'm assuming that the other 2 are a ?relay? that gets tripped by the t-stat.
So what part am I looking for in that case?
thanks again for your patience.
Jeff
I know 2 are line, 2 are load, and I'm assuming that the other 2 are a ?relay? that gets tripped by the t-stat.
So what part am I looking for in that case?
thanks again for your patience.
Jeff
Hi Jeff,
If you look closely, you'll see that your transformer has only 4 spades as well.
On two of them will be a double spade connector allowing two wires to be connected there.
Remove the connector with the two wires and connect the same way to new transformer.
Thanks,
Robert
If you look closely, you'll see that your transformer has only 4 spades as well.
On two of them will be a double spade connector allowing two wires to be connected there.
Remove the connector with the two wires and connect the same way to new transformer.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I measured the voltage on the blower relay then.
with Cool set to On, Fan set to On, and t-stat at 65, I still have no voltage on contact 1 & 3 which are the wires running to the blower motor.
So is the blower relay my problem then, or is something else more likely?
Jeff
with Cool set to On, Fan set to On, and t-stat at 65, I still have no voltage on contact 1 & 3 which are the wires running to the blower motor.
So is the blower relay my problem then, or is something else more likely?
Jeff
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Kicking the skirting venting dead-horse, again
by mdnagel » Sun Jul 07, 2019 1:37 pm » in Mobile Home Repair - 10 Replies
- 31660 Views
-
Last post by mdnagel
Sun Aug 11, 2019 3:47 pm
-
-
-
Need advice on blower
by NorthTexasSafariGuy » Mon Jul 31, 2017 9:18 am » in Coleman Service & Repair - 0 Replies
- 70775 Views
-
Last post by NorthTexasSafariGuy
Mon Jul 31, 2017 9:18 am
-
-
-
Blower fan acting up 7995-656/d
by Michael Yep » Fri Oct 06, 2017 11:26 am » in Coleman Service & Repair - 0 Replies
- 36496 Views
-
Last post by Michael Yep
Fri Oct 06, 2017 11:26 am
-
-
- 0 Replies
- 57618 Views
-
Last post by Montanan
Wed Jan 03, 2018 1:03 pm
-
-
LOUD Blower on Coleman Presidential 2 900759
by AuntKatie » Thu Apr 05, 2018 6:50 pm » in Coleman Service & Repair - 0 Replies
- 44880 Views
-
Last post by AuntKatie
Thu Apr 05, 2018 6:50 pm
-