I have a Coleman DGATO56BDD furnace. Trouble light is blinking 4 times. I believe this means the limit switch is bad or one of them because I heard there was more then 1. My question is where are the limit switches and how to replace them. Furnace will run for a short period but the blower will shut off before the house reaches the right temperature.
Hi,
Yes, 4 flashes means a limit is cycling. One is on back wall of control box and the other is on left side about midway up under the blower section.
Both should be closed at all times and should show continuity when ohmed with wires disconnected.
To replace, you remove wires, remove screws, mount new switch and replace wires.
Those are safeties, so you should get furnace checked by an hvac tech as they may be doing their job and opening due to a problem within furnace.
Thanks,
Robert
Yes, 4 flashes means a limit is cycling. One is on back wall of control box and the other is on left side about midway up under the blower section.
Both should be closed at all times and should show continuity when ohmed with wires disconnected.
To replace, you remove wires, remove screws, mount new switch and replace wires.
Those are safeties, so you should get furnace checked by an hvac tech as they may be doing their job and opening due to a problem within furnace.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Posts: 3
- Joined: Sun Oct 11, 2009 10:01 am
Ok, I replaced both limit switches and it is still doing it. Any other ideas. Thanks
-
- Posts: 3
- Joined: Sun Oct 11, 2009 10:01 am
Unfortunately I cannot afford a repair man at this time and its still doing it. I have to keep turning the main switch off which resets it. I'm thinking the control board or blower inducer. What troubleshooting can I do myself.? It still blinks 4 flashes and I have replaced both limit switches.
Hi,
As previously stated, IF it is flashing a limit open code and you replaced the limits and it is still doing it, then they may be doing their job.
The furnace needs to be inspected to ensure there is not a safety hazard causing this.
To continue turning off and on and resetting it is raising the risk of a fire IF there is a problem.
Find someone or an organization to either inspect it or help you pay to have it inspected and diagnosed.
THEN, if the fix is a DIY one, repair it and have peace of mind knowing you are warm and safe.
Take care and best wishes,
Robert
As previously stated, IF it is flashing a limit open code and you replaced the limits and it is still doing it, then they may be doing their job.
The furnace needs to be inspected to ensure there is not a safety hazard causing this.
To continue turning off and on and resetting it is raising the risk of a fire IF there is a problem.
Find someone or an organization to either inspect it or help you pay to have it inspected and diagnosed.
THEN, if the fix is a DIY one, repair it and have peace of mind knowing you are warm and safe.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 0 Replies
- 110107 Views
-
Last post by cwwhite75
Sat Feb 29, 2020 8:46 am
-
-
Colman evcon presidental 7980B856 furnace will not stay on
by ezridersid » Sat Dec 21, 2019 8:52 pm » in Mobile Home Repair - 1 Replies
- 17314 Views
-
Last post by ezridersid
Sat Dec 21, 2019 9:04 pm
-
-
-
Transformer burning out in an Evcon DES 80
by BigDave67s » Wed Dec 29, 2021 10:01 pm » in Coleman Service & Repair - 0 Replies
- 112053 Views
-
Last post by BigDave67s
Wed Dec 29, 2021 10:01 pm
-
-
-
Evcon Heat Pump - Air Conditioner Model No. BRHS036B Making HUM Before Starting
by Dave_L » Tue Aug 29, 2023 1:26 am » in Coleman Service & Repair - 0 Replies
- 126607 Views
-
Last post by Dave_L
Tue Aug 29, 2023 1:26 am
-
-
- 0 Replies
- 57618 Views
-
Last post by Montanan
Wed Jan 03, 2018 1:03 pm