condensor hums

Posted: Sat May 12, 2007 12:14 am
by noltingj
Coleman Presidential III Heat/AC unit

When the blower kicks on to cool, the condensor unit outside hums very loudly and the fan inside doesn't move. We had a pretty bad storm come through our area (southeastern SD) last weekend, so I went to check to see if a fuse had blown, but found that there is no fuse at all on the condensor. There's no shut off switch other than turning off the breaker. Is there anything else I can look for before calling in a professional?

RE: condensor hums

Posted: Sat May 12, 2007 1:18 am
by hvac1000
More than likely the condenser fan motor is shot. It could also be a capacitor for the motor is also shot. Do you have the model number of the outside unit. If you feel up to it we do have motors available.

The unit should have a disconnect outside for safety. You might consider having one of those installed.

I will not work on out door A/C units without a disconnect. It is just not safe.

RE: condensor hums

Posted: Mon May 14, 2007 7:16 am
by noltingj
The model number of the condensor is 9530F901.

How much would it cost to fix this? Would it be better to just get a new system installed since this one is probably from the mid 80s?

RE: condensor hums

Posted: Mon May 14, 2007 12:09 pm
by hvac1000
I have had no luck with your model number. What is the brand?

As far as replacement goes you will have to replace your inside coil and the outside unit at the same time. Almost all newer 13 SEER units require a new coil for them to work correctly. Now you can add a Expansion valve but you still will not get the efficiency you are paying for.

Get me the name of the unit and look for a better model number.