First question: In heat mode the heating element appears to function but fan does not come on when the switch is on auto. When the switch is flipped to ON the fan appears to work fine. I'm assuming this is a sequencer problem after reading similar posts of other models? Can you verify and point me to the correct replacement part as I seem unable to locate it?
2nd question: is there a service manual for this model that we can download, one was not provided with the home and we are unable to locate one.
thanks.
Intertherm E1EH-015ha
Hi,
1.)- Sequencer # 01-0840 ( Controls blower and 2 elements)
Sequencer # 621383 (Controls third element)
I recommend replacing both when one fails.
2.)- Furnace homeowners manual can be ordered here :
http://www.hvacmanuals.com/
Thanks,
Robert
1.)- Sequencer # 01-0840 ( Controls blower and 2 elements)
Sequencer # 621383 (Controls third element)
I recommend replacing both when one fails.
2.)- Furnace homeowners manual can be ordered here :
http://www.hvacmanuals.com/
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi,
Call toll free to 1-877-263-7860 and speak with Mark. I believe the older FEH furnaces were real close/similar to the E1EH.
Then the E2EH is just the next series and very similar also.
You're very welcome, happy to help.
Thanks,
Robert
Call toll free to 1-877-263-7860 and speak with Mark. I believe the older FEH furnaces were real close/similar to the E1EH.
Then the E2EH is just the next series and very similar also.
You're very welcome, happy to help.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
New problem,
We fixed the inside heater with a relay (621867 Relay), we didn't replace the sequencers as the relay was testing bad and when we replaced that the inside heater works as expected. However, we noticed that the outside heat pump does not come on. We did test the A/C and the outside unit comes on and works, blows cold air as expected when the thermostat is in cool. Any suggestions on why the heat pump is not coming on when the thermostat is on heat?
Outside Unit Brand: Goodman
Outside Unit Model Number: CK42-1C
thanks,
We fixed the inside heater with a relay (621867 Relay), we didn't replace the sequencers as the relay was testing bad and when we replaced that the inside heater works as expected. However, we noticed that the outside heat pump does not come on. We did test the A/C and the outside unit comes on and works, blows cold air as expected when the thermostat is in cool. Any suggestions on why the heat pump is not coming on when the thermostat is on heat?
Outside Unit Brand: Goodman
Outside Unit Model Number: CK42-1C
thanks,
Hi,
Could be the t-stat, defrost board, reversing valve, reversing valve solonoid. Would need all tested and checked to see what is not allowing the switch to heat mode.
Thanks,
Robert
Could be the t-stat, defrost board, reversing valve, reversing valve solonoid. Would need all tested and checked to see what is not allowing the switch to heat mode.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
So we cracked the heat pump and all we found inside was a capacitor, relay/contactor, fan, compressor, cooling lines. The unit clearly states it is a heat pump on the model information tag, but there is no defrost board or other control electronics in the outside unit. There are 2 wires that lead from the coil of the relay/contactor to the system indoors. That's the only low voltage circuit connection that there is. We tested low voltage when the t-stat (honeywell ct31a1003) was in cool mode and the unit outside was running there is 24v to the relay/contactor coil. In heat mode there is no voltage to relay/contactor coil, the question is why? As far as we can tell the relay/contactor coil is connected to one output on the t-stat (there are 4 wires, only the yellow wire goes to the outside unit), there are no other connections from the t-stat to the heat pump. T-stat appears to be completely functional except there is no 24v to the heat pump in heat mode.
Is it possible there is not supposed to be any voltage to the heat pump in heat mode or that the fan is not supposed to run in heat mode? Is it really working like it's supposed too or is really not a heat pump at all? We are confused....
Is it possible there is not supposed to be any voltage to the heat pump in heat mode or that the fan is not supposed to run in heat mode? Is it really working like it's supposed too or is really not a heat pump at all? We are confused....
Hi,
What is the outside unit brand name and model number ?
IF you look inside outside unit and follow both refrigerant lines (big and small one) where they enter the unit, then go to compressor, then to the coil around unit, then from coil come around and exit unit to go inside home.
Do you see a component with 3/4/5 lines connected to it and a solonoid and wires coming to it and it is in the refrigerant line ?
If not and you just have two plain copper pipes/lines with nothing installed in one, then it is not a heat pump.
You would also have an orange wire connected at t-stat and running out to unit.
Thanks,
Robert
What is the outside unit brand name and model number ?
IF you look inside outside unit and follow both refrigerant lines (big and small one) where they enter the unit, then go to compressor, then to the coil around unit, then from coil come around and exit unit to go inside home.
Do you see a component with 3/4/5 lines connected to it and a solonoid and wires coming to it and it is in the refrigerant line ?
If not and you just have two plain copper pipes/lines with nothing installed in one, then it is not a heat pump.
You would also have an orange wire connected at t-stat and running out to unit.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
that's what we thought, should have more wires.
we tested voltage to the unit from the t-stat lines - there is 24v in A/C mode but nothing in heat mode. we are at the conclusion that either this has not been wired to use as a heat pump or despite what the label says it is not a heat pump.
thank you for your help, I will post after we look at the coolant lines.
we tested voltage to the unit from the t-stat lines - there is 24v in A/C mode but nothing in heat mode. we are at the conclusion that either this has not been wired to use as a heat pump or despite what the label says it is not a heat pump.
thank you for your help, I will post after we look at the coolant lines.
Hi,
Could be heat pump with a bad reversing valve keeping it in cooling mode. Someone may have disconnected wires for heating and just used electric furnace inside, making the heat pump a straight a/c unit.
Been done a time or two. Then it may not be a heat pump.
Thanks,
Robert
Could be heat pump with a bad reversing valve keeping it in cooling mode. Someone may have disconnected wires for heating and just used electric furnace inside, making the heat pump a straight a/c unit.
Been done a time or two. Then it may not be a heat pump.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I think we've determined finally that the outside unit is not a heat pump, unfortunately. I guess we are going to look into installing a heat pump or replacing the entire system, or finding an alternative. Have any recommendations on where to look for heating/a-c systems for mobile homes and what size we should get, I think the home is 1100 sq ft? thank you for all you help!
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne Mod. E1EH-015HA split unit/eliminate cooling?
by carolina jim » Thu Oct 24, 2019 8:33 am » in Nordyne Service & Repair - 0 Replies
- 39441 Views
-
Last post by carolina jim
Thu Oct 24, 2019 8:33 am
-
-
- 0 Replies
- 78422 Views
-
Last post by newguy47
Thu Aug 16, 2018 8:21 pm
-
-
heater blower intertherm feh-015ha-03
by newguy47 » Wed Oct 24, 2018 8:04 am » in Nordyne Service & Repair - 0 Replies
- 84810 Views
-
Last post by newguy47
Wed Oct 24, 2018 8:04 am
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167397 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
intertherm feh-015ha-04 Noisy Blower
by kjaxes99 » Sat Oct 24, 2020 4:45 am » in Nordyne Service & Repair - 0 Replies
- 141439 Views
-
Last post by kjaxes99
Sat Oct 24, 2020 4:45 am
-