Hello, I have a Nordyne unit in my mobile home(sorry don't have the model # right now as I just found this site, will have it tonight!) and the heat will not work in the "Auto" mode or "Fan" mode, only when I turn it to "Vent" do I get any heat! Although all of these modes work perfectly fine with the AC! The only way I can get any heat is to have it in "vent" mode and turn to heat. If I select auto mode and heat, I can move the temp selector switch up and down and I hear something click like it wants to come on but it never does?? This is the first time I have used my heat this year. I can get heat using the "vent" but this runs all the time and I don't want to leave it continuously running! Thanks so much for any help, its getting cold and i need my heat! Thanks for any advice!
Eric
UPDATED**Nordyne/ No heat in auto-only in vent mode??
Hi Eric,
That's your evaporator a-coil number. Look on facing of furnace midway or down lower for a data sticker or nameplate.
Thanks,
Robert
That's your evaporator a-coil number. Look on facing of furnace midway or down lower for a data sticker or nameplate.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Eric,
Do you feel any heat around furnace ? Like maybe one or more elements are energizing, but no blower or is nothing at all coming on.
You should be able to feel heat around the furnace if any elements are on.
Thanks,
Robert
Do you feel any heat around furnace ? Like maybe one or more elements are energizing, but no blower or is nothing at all coming on.
You should be able to feel heat around the furnace if any elements are on.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Eric,
Possibly a bad sequencer, but need to see if it is getting 24vac across (front to back) the bottom H terminals of sequencer from T-stat.
If so and no elements or blower, sequencer is bad.
Thanks,
Robert
Possibly a bad sequencer, but need to see if it is getting 24vac across (front to back) the bottom H terminals of sequencer from T-stat.
If so and no elements or blower, sequencer is bad.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Eric,
Ok, your furnace does not have any sequencers, it uses contactors and relays for the heating element and blower controls.
The circuit runs through each and without tracing each circuit, hard to know which one may be at fault from here.
Contactor # 621957
Contactor # 621958
Relay # 621898
Relay # 621899
Depending on what excatly is or is not working at the given times needed, could be just one, a combo of two or more or none at all.
However, usually, one or more is the fault with problems as you described.
They can all be seen and ordered through PayPal from this page :
http://www.mobilehomerepair.com/NordyneElec.html
Prices are listed and shipping is $8.00 .
Thanks,
Robert
Ok, your furnace does not have any sequencers, it uses contactors and relays for the heating element and blower controls.
The circuit runs through each and without tracing each circuit, hard to know which one may be at fault from here.
Contactor # 621957
Contactor # 621958
Relay # 621898
Relay # 621899
Depending on what excatly is or is not working at the given times needed, could be just one, a combo of two or more or none at all.
However, usually, one or more is the fault with problems as you described.
They can all be seen and ordered through PayPal from this page :
http://www.mobilehomerepair.com/NordyneElec.html
Prices are listed and shipping is $8.00 .
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hey Robert, need your help again!?
Ok, I went ahead and replaced both relays and both contactors that you mentioned and the heat still will not work in auto mode! Here is what is happening, as I said, I can only get some heat in the "Vent" mode. Now that I have replace the contactors and relays, I can switch the unit to "Heat" and "Auto" and I see the elements heat up but then something clicks and it goes out, the fan never runs in this mode although I did once see it try and spin. So there is heat at the elements but it just wont come on and run?? Any ideas on what else could cause this?? Im sure its not the blower cause it works fine but I can't get the heat to work in "auto" mode, and its really cold
here? Please help!? Thanks alot!!
Ok, I went ahead and replaced both relays and both contactors that you mentioned and the heat still will not work in auto mode! Here is what is happening, as I said, I can only get some heat in the "Vent" mode. Now that I have replace the contactors and relays, I can switch the unit to "Heat" and "Auto" and I see the elements heat up but then something clicks and it goes out, the fan never runs in this mode although I did once see it try and spin. So there is heat at the elements but it just wont come on and run?? Any ideas on what else could cause this?? Im sure its not the blower cause it works fine but I can't get the heat to work in "auto" mode, and its really cold
![Sad :(](./images/smilies/icon_sad.gif)
Hi,
First, look everything over closely with wiring diagram and be sure all is wired correctly.
Then if the motor still won't work, set t-stat at heat-auto-85* and go to motor wiring harness.
Follow it to the molex connector plug. Look at where the Yellow wire and Orange wire goes, unplug the connector and find corresponding holes for those two wires, yellow and orange.
Place one meter lead in each and see if you have 240VAC there.
Do this test about 1 to 2 minutes after call for heat from t-stat.
IF you do not have it there, you will need to follow circuit going by wiring diagram and check backwards to find where the power is stopped at.
Thanks,
Robert
First, look everything over closely with wiring diagram and be sure all is wired correctly.
Then if the motor still won't work, set t-stat at heat-auto-85* and go to motor wiring harness.
Follow it to the molex connector plug. Look at where the Yellow wire and Orange wire goes, unplug the connector and find corresponding holes for those two wires, yellow and orange.
Place one meter lead in each and see if you have 240VAC there.
Do this test about 1 to 2 minutes after call for heat from t-stat.
IF you do not have it there, you will need to follow circuit going by wiring diagram and check backwards to find where the power is stopped at.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hmm, I'll check that Robert. If I am getting 24vAC there, is there any chance it could be something with the run capacitor? Cause the only thing left if the motor and I'm sure its fine cause it works fine when the "vent" is running and also works fine in "cool" A/C mode! Thanks for your help, I'll keep trying.
Hi,
240VAC, not 24VAC . If run capacitor was bad, motor would not work in any mode.
The motor runs a different circuit for heat-auto than it does for a/c-auto and fan ON modes.
Thanks,
Robert
240VAC, not 24VAC . If run capacitor was bad, motor would not work in any mode.
The motor runs a different circuit for heat-auto than it does for a/c-auto and fan ON modes.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hello Robert, just a thought, if I wasn't getting the 240vac, the transformer would be bad right, but I wouldn't think that cause the blower actually does run and work, just not in "Heat"-"auto" mode.Also as per the wiring diagram, if you said to check for 240vac across the yellow and red on the molex plug, the red is not use,it isn't connected to anything, it just hangs down with a female spade end on it, the yellow I beleive goes to one of the relays. Sorry to have so many questions but I really wanna get this fixed and I'm running out of ideas, if both relays and both contactors have been replaced, just don't know what else it could be??? I've checked the wiring twice, as I looked at it last night, like I said, I can watch the elements heat up and come on, then both contactors click and it shuts off, then repeats this process again in minute or so but no blower ever comes on, since the blower will work, it wouldn't be a problem with the motor would it?? Thanks Robert!
"Determined to get this fixed"!!![Very Happy :D](./images/smilies/icon_biggrin.gif)
"Determined to get this fixed"!!
![Very Happy :D](./images/smilies/icon_biggrin.gif)
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167398 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Eb15a elec furnace will only come on if jumpered at themostat
by redcat31 » Wed Jan 31, 2018 6:18 pm » in Service & Repair of Other Brands - 0 Replies
- 23402 Views
-
Last post by redcat31
Sat Feb 03, 2018 1:20 am
-
-
- 1 Replies
- 3586 Views
-
Last post by Greg
Sun Oct 14, 2018 8:41 am
-
-
Doublewide - Vent or Leave roof Non-vented?
by 73Viking » Fri Jun 14, 2019 7:00 pm » in Mobile Home Repair - 2 Replies
- 11568 Views
-
Last post by 73Viking
Sat Jul 13, 2019 12:21 pm
-
-
- 3 Replies
- 3187 Views
-
Last post by Greg
Thu Aug 22, 2019 6:56 pm