Coleman 3400A816 Central Electric (no heat)

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
BerryCreek
Posts: 1
Joined: Tue Dec 15, 2009 12:04 am

The furnace is about 20 years old. The moblie home it was installed in is our vaction home so it had low usage through out its lifetime. Quite some time ago it started putting out much less heat. It still puts out a small amount of heat, but it takes several hours to notice a slight rise in temperature. What do i need to do to get this issue resolved. :|
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

Need to determine whether all the element coils are receiving power.

If not, then need to find break in power.

If they are, then need to see if the element coils are working or not.


You will need a volt meter and having an ammeter would be great also.


I offer email instructions on doing this if needed for a $20 fee. Can send a link for paying if needed, just let me know.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?