EB15C RUNNING CONSTANTLY

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
unclebuckaroo
Posts: 2
Joined: Fri Jan 01, 2010 1:15 pm

Hi,
Have a coleman electric furnace Model EB15C, that is about 3 yrs old. Furnace blower and maybe one heater element runs even though thermostat is disconnected. Can only turn off with main breakers. Could this be a faulty sequencer?
David
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi David,

Most likely the sequencer.

Sequencer # 3115 - 3571 can be seen and ordered through PayPal from right side of this page:

http://www.mobilehomerepair.com/ColemanElec.html




Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
unclebuckaroo
Posts: 2
Joined: Fri Jan 01, 2010 1:15 pm

Robert,
Thanks for the fast response. Seems to be a common problem for these units. Are all sequencers equal in quality, since this one did not see much use?
Dave from virginia
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

Yes, fairly common for sequencers and a/c contactors where you have switching contacts that arc, pit and wear.


They're all about the same except for the different timing sequences, need that to be compatible.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?