ColemanDGAT070BDG
Posted: Thu Feb 04, 2010 9:50 pm
I have a 1994 model furnace that when thermostat calls the furnace goes through pre-purge, the ignitor glows and the main burner lights. After a short period of time the gas valve starts clicking and does this for a random amount of time and will eventually go out. I have replaced the module, gas valve and cleaned the flame senser. When I trouble shoot the module, I have 94 volts present at the flame sense terminal and when the burner is lit when I go from this terminal to ground, the flame goes out everytime....where do I go next