3500a816 coleman electric furnace

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
stumped59
Posts: 2
Joined: Fri Mar 19, 2010 6:44 pm

i have replaced t-stat,fan relay switch along with the tranformer,sequencer and limit switches but the blower still runs but at a much lower rpm after the furnace shuts down it heats normal and the ac cools normal.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Can you clarify that somewhat, a little confusing about the "after furnace shuts down" part ?


Try replacing the run capacitor if it has one on the side/top of the blower housing. That will cause it to run slow if it is bad.


Also be sure that you have 240vac at the blower leads molex plug connection to the motor.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
stumped59
Posts: 2
Joined: Fri Mar 19, 2010 6:44 pm

What i mean by after furnace shuts down the blower motor continues to run but at a lower rpm. This furnace has no capacitor i had the central air added later everything worked fine until the last couple of weeks.