Condenser Fan inop

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
brcidd
Posts: 2
Joined: Tue May 04, 2010 6:12 pm

So my MIL calls says its hot in her mobile home-- I discover condenser fan not working- go ahead and kick start it-- it works for about a week--she calls again- I then pull out motor- inject oil into the oil holes- it works for about a 1/2 day-- she calls again.

Fan motor is an Emerson model 1468-211 1/3 hp 208-230V 1100 rpm

what is most likey wrong-- fan motor worn out, or capacitor shot? How should I test? Unit is pushing twenty years old. Thanks for your input
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

Test to see if you are getting full voltage to the two motor leads. Was the motor hot when it quit ?

Check the run capacitor to see if it is swollen, bulging, leaking.

Could replace the run cap to see if it helps, would have to replace it anyway if you replaced the motor.




Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
brcidd
Posts: 2
Joined: Tue May 04, 2010 6:12 pm

Motor was not running when it quit-- won't start---

Put in a new run capacitor-- runs fine now

Thanks for your help